code for pex water line crossing electrical?

mikec35

Well-known member
Joined
Jun 17, 2011
Messages
1,258
Location
NC
is there a code for this? My water line will either need to run up the wall and cross my electrical or possibly run perpendicular under my electrical line by a couple of inches. Any advice? Thx
 
To avoid these ads, REGISTER NOW!

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
we cross paths all the time. the rule is that if there will be galvanic corrosion problems ie copper pipe touching aluminum or steel conduit or cable then you have to wrap one or the other to isolate them other than that just use common sense.
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
cant go over top of electrical panel and stay 1 foot away all way around.
I'm not sure what code this is you are referring to (this 1 foot rule), but it's not in the NEC or any local code I have ever heard of.

There is NO separation code from water piping, especially Pex. I'm not sure where this urban legend code got started.
 
OP
M

mikec35

Well-known member
Joined
Jun 17, 2011
Messages
1,258
Location
NC
Thanks for the replies, I am going to run a water line for an outside spigot and it will be very close to my existing electrical, wasn't sure if I could go over or under the wire, didn't want to do anything that was unsafe that I would have to undo later.
 

tylernt

Well-known member
Joined
Jan 24, 2013
Messages
182
Location
Idaho, US
I'm not sure what code this is you are referring to (this 1 foot rule), but it's not in the NEC or any local code I have ever heard of.
Agreed. uniballer is probably referring to 110.26(E)(1) which disallows water pipes over a distribution panel unless provided with something like a drip pan, but there is no issue (that I'm aware of) with pipes and wires away from the panel.
 