I'm not sure what code this is you are referring to (this 1 foot rule), but it's not in the NEC or any local code I have ever heard of.cant go over top of electrical panel and stay 1 foot away all way around.
Agreed. uniballer is probably referring to 110.26(E)(1) which disallows water pipes over a distribution panel unless provided with something like a drip pan, but there is no issue (that I'm aware of) with pipes and wires away from the panel.I'm not sure what code this is you are referring to (this 1 foot rule), but it's not in the NEC or any local code I have ever heard of.