Code question on knockout connector size for main feed cable

1233user

Well-known member
Joined
Dec 6, 2011
Messages
360
Location
CT
I have a 2/0 SER aluminum feed cable going to the sub panel in my garage. Is there anything in the electrical code about what size connector it has to go through entering the panels? It will fit through a 1 1/2", I just want to make sure that I don't need a larger size to meet code. Thanks.
 
To avoid these ads, REGISTER NOW!
OP
1

1233user

Well-known member
Joined
Dec 6, 2011
Messages
360
Location
CT
No. Whatever the correct fitting is will determine the KO size.

The knockout in the panel for the main feed is multiple sizes, so I can punch it out as big as needed to fit the correct size connector.
 

Attachments

  • 20140727_144841.jpg
    20140727_144841.jpg
    108.5 KB · Views: 7
Last edited:
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Halex 1½ NM/SE cable clamp

Indoors Only. Fits NM Cable: Flex cords, multi flex cords; fitting range .834-1.520 inches diameter SE cables 2 conductor 4/0. Type: Twin Screw. In a dry location, use to connect nonmetallic sheathed cable to a steel outlet box or other metal enclosure. Miscellaneous: 1-1/2" knockout.
 