I've been reading up on the dangers/unwisdom of using coiled power cords. How do power cord hose reels function well enough if this is a danger? I have a 5-gal bucket with 100' of 12ga extenion cord wrapped around a coffee can in it. I've never had any problems with the cord overheating when I only pull out enough to reach (rarely ever the full length) and I never even noticed it getting warm enough in the bucket to soften up like after it's exposed to the sun's heat. It's only ever really used in intermittent power tool use, not in a continuous draw.

Anyhow, I'll be purchasing some 25' and 50' lengths of 10ga extension cords in about two weeks. :D
 
To avoid these ads, REGISTER NOW!

big.jim

Well-known member
Joined
May 11, 2011
Messages
1,011
Location
derbyshire uk
coiled up downgrades the load carrying capacity of the cable by about 35%,so a 10a cable coiled is actually a 6.5a cable ,but is for continuous rating before it will overheat
 

pacmktg

Well-known member
Joined
Mar 1, 2009
Messages
297
Location
Foothills of CA
I sell reels for Coxreels. They make heavy duty industrial grade cord and cable reels along with hose reels. It states in the instructions to fully extend the electrical cord before using except on the 16-3 models. On the welding Cable reels, it states that they must be fully extended before using.

The danger is heat build up and fire.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
I sell reels for Coxreels. They make heavy duty industrial grade cord and cable reels along with hose reels. It states in the instructions to fully extend the electrical cord before using except on the 16-3 models. On the welding Cable reels, it states that they must be fully extended before using.

The danger is heat build up and fire.

This is the right answer. When using cord reels just pull all the cord out when using at higher loads.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I am always curious, why 25 ft of number 10? What tools are you guys running with only a bit of 100 ft of cord uncoiled out of a bucket?
 

the gypsy

Well-known member
Joined
Mar 13, 2013
Messages
1,780
Location
Montreal, Quebec, Canada
I read this a few times. I wonder if it is because of the thin insulation on the newer cords that are made overseas, or if applies to all cords regardless if the insulation is thick or thin?
 

Syberia

Well-known member
Joined
Jan 13, 2014
Messages
1,451
Location
Perris, CA
I am always curious, why 25 ft of number 10? What tools are you guys running with only a bit of 100 ft of cord uncoiled out of a bucket?
Portable air compressor, or 120v welder being used on the breezeway outside my garage.
 
OP
R

rick carpenter

Well-known member
Joined
Jan 20, 2011
Messages
3,825
Location
Huntsville, East Texas
I am always curious, why 25 ft of number 10? What tools are you guys running with only a bit of 100 ft of cord uncoiled out of a bucket?

The 100' of 12ga is the only good heavy-duty extension cord I have for home use, but I use it for disaster clean-up/rehab/rebuild too. I may go with two 25' 10ga cords, to be bought primarily for disaster work in mind where you don't know what or how many things you'll need to power (better to be overprepared than underprepared), but I'll use them as well as at home. They'll be easier to transport and only a little less flexible handling than the 12ga.
 