I am working on a communication signal for a fire suppression system. The signal is 24VDC circuit. The pulses on a oscilloscope will only dip to a low of +18VDC. So a pulse height of only 6VDC. Is this common and how is this possible to dip only 6 volts and not the full 24volts? If so what kind of communication style is this? It is hooked up as a 2wire daisy chain similar to a RS485 loop or profibus. Any insight would be great.
 
To avoid these ads, REGISTER NOW!

plow

Well-known member
Joined
Feb 12, 2013
Messages
1,024
Location
Louisiana
What circuit are you reading? What system? What are you trying to accomplish? Is it conventional or addressable?
 

kaffine

Well-known member
Joined
Dec 13, 2009
Messages
3,610
Location
Henderson, NV
I am not familiar with RS485 or profibus so this may not be valid.

One of the modules on the daisy chain has failed and supplying constant power to the chain. When another module tries to transmit data it can not sink enough current to bring the voltage level down to 0. Could also be there is another signal shorted to the bus somewhere supplying power. Could try and disconnecting modules one by one to see if the problem goes away.

The other thing is does 485 or profibus require terminating resistors? Perhaps one or more of the resistors is missing or failed.

Is RS485 or profibus a single ended signal or a differential signal? If differential are you comparing the signals or are you referencing a ground?

Again I said I am not familiar with rs-485 or profibus so I am just assuming the values are wrong and it should be dropping the voltage down to 0V
 

ironmutt

Well-known member
Joined
Jul 24, 2012
Messages
354
Location
Ill.
i might be wrong but i am pretty sure if your just reading voltage you may not have the right osilliscope . if the signal is pulsing fast enough it will look like only a slight drop in volts even though it is going full off and on it is so fast the machine cant read it
 

plow

Well-known member
Joined
Feb 12, 2013
Messages
1,024
Location
Louisiana
It sounds like he may be reading supervisory current. That is IF I'm "on the same wave length" as him (pun intended).
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
I am not familiar with these systems at all, so all I can offer is to be sure you are AC coupled to the signal and you are not looking at any DC sealing potential that may be present, and not allowing you to see the full voltage swing. Direct probe or 10x probe?
 
To avoid these ads, REGISTER NOW!

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
you can engineer a signal level to be anything you want. these protocols with fire alarms and suppression are often proprietary to the manufacturer. can they offer any insight on this?
 
OP
R

r_olson_06

Well-known member
Joined
Feb 12, 2012
Messages
4,160
Location
SD
Called manufacture on the signal and found out very little on the signal. With a noise level running about 10VAC (peak to peak) for a duration of 10ms and re-ocurring every 200-250ms sound like a noise issue. Also with the manufacture saying this signal is really prone to noise installed on a system with 20+ Servo Drives. Sounds like Trouble.
 

plow

Well-known member
Joined
Feb 12, 2013
Messages
1,024
Location
Louisiana
By code it has to be UL listed. If something bad happens, Its yo baby. DACT units are cheap. Good luck.

Phillip out
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
if it occurs regularly try to find the source of the noise by turning off equipment one at a time until the noise clears. you may need to isolate the cable in piple and use shielded cabling to null out the noise.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
By code it has to be UL listed. If something bad happens, Its yo baby. DACT units are cheap. Good luck.

Phillip out

A code cannot require UL or other specific listing, they merely require listing which is understood as listing by a NRTL, Nationally Recognized Testing Laboratory which UL is one. Requiring a specific NTRL by a code means lawsuit time.
 

Rob_b

Well-known member
Joined
Jul 28, 2009
Messages
209
Location
Ontario Canada
quick question...what type of cable are you using for this RS485/profibus line? It should be a twisted shielded pair(beldon) with the shield landed on ground at one end only as a drain. You can't run this cable with any other current carrying conductors in a conduit. I work with RS485/DH+ every day and it can be a PITA to track noise.
 