Hi Gang.
I bought this unit at auction and had it wired to the panel.
Its a 10HP 3 phase motor that was wired for high voltage when I bought it(460V).
We rewired it for 220v.40 amp
installed a new switch.
When we turn on the switch at the control box, the box just hums.
No sound from the motor at all.
The motor and pump spin freely.
Is there a different wire sequence in the control box that needs to be adjusted from 460v back to 220v as well?
Please see attached pics for reference.
Thanks
Tim
 

Attachments

  • IMG_3087.jpg
    IMG_3087.jpg
    74.8 KB · Views: 31
  • FullSizeRender.jpeg
    FullSizeRender.jpeg
    29.9 KB · Views: 31
  • IMG_3135.jpg
    IMG_3135.jpg
    109 KB · Views: 34
  • IMG_3096.jpg
    IMG_3096.jpg
    99.8 KB · Views: 31
  • IMG_3101.jpg
    IMG_3101.jpg
    82.2 KB · Views: 27
Last edited:
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,827
Location
NW Iowa
Coil is 480v. Starter probably isn't big enough for that motor on 240v anyway
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,773
If 480V it's probably a Size 1 starter.
At 240 it would require a Size 2 starter.

Worked on a 10 HP 240V cardboard baler that had a OEM NEMA size 1 Joslyn Clark starter, vaporized the contacts after a number of years, causing it to single phase.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,767
Location
SE Michigan
Thanks Bert!
Best just to leave it wired for 480v instead of swapping out the coil ?

Do you have 480vac service available?

If so I would use that, much lower amp draw.

But, if your service is 240vac then as Bert said you need a motor starter with a 240vac coil OR you could use a 480:240 dry transformer in reverse to step up the control voltage to 480vac.

Best advice is to create some as-built wiring diagrams and put them inside of the panel once you get it working. Someday they will come in very handy.
 
OP
T

Twisted Rock

Member
Joined
Jan 25, 2021
Messages
6
Location
Alberta
Hi guys
Thanks for all the advice.
I’m sure we have 600v service to the bay transformer
I’ll double check tomorrow
The electrician said he wired it 3 phase 240 with 40 amp
It does have a 480v coil installed so I either need to get 480v to the compressor and wiring the motor back to high voltage or swap out the coil and starter for 240v
 