Compressor disconnect- recommendations wanted
iceman510
I am preparing to wire in my compressor. It is a 5 hp so as I have learned here, it needs to be wired in directly and I need a disconnect (in a different room than the breaker box).
Question is, does this disconnect need to be fused? I suspect it doesn't since it is on it own breaker. I don't particularly like the pull-out disconnect type like is often used for A/C installations, but they seem the cheapest. Recommendations or suggestions for a type to use? I was thinking something like this:
http://www.menards.com/main/electrical/circuit-protection-distribution/safety-switches-disconnects/ge-30-amp-indoor-non-fused-safety-switch/p-2289756-c-6435.htm
Fusible type is much cheaper.
Thanks for any input.
freshintulsa
Tulsa, OK
I just wired up my 7.5 hp compressor and used the square d one in the link that pattenp posted. works great and its cheap!
I
iceman510
That looks great. Must have missed that one. Now, I am planning a 30 A breaker in the box since the motor is only rated at 15A. The 60 for this won't matter because it is not a breaker, correct? That is just the rated capacity?
U said your compressor is 5HP? A 5HP motor should have an FLC close to 28a. If your comp lists 15a then the HP rating is bloated...If your compressor is truly rated at 5HP, thrn a 30a breaker may suffer from nuissance tripping due to in-rush currents...
I
iceman510
Perhaps a bit of bloating...
In the previous house I had no nuisance tripping on a separate box in the garage with a 30A breaker and it plugged into a wall socket with a cord. Not sure if that was ok then, but did that back in 1999, and if wrong I didn't know any better.
Now I expect it to work fine and it will be direct wired. I can still use the cord wire with the plug end removed to direct wire it, correct?
Is FLC "full load current"?
Norcal
Nope, use sealtite or metal flex, (Greenfield), a cord is not supposed to be a substitute for permanent wiring.
I
iceman510
So if I am understanding that correctly (and table 430.248 that I found), the FLC of 28 means I should use at least 10 AWG correct? I have some of that wire and found an appropriate length of BX (which I believe is what is referred to by the name Greenfield above). With the disconnect mentioned above, I should be good to go.
Sick of using my 4 gallon pancake that can't power anything but nailers.
Thanks all.
Norcal
BX is slang for armored cable, greenfield is slang for flexible metallic conduit, BTW the stuff they sell in the big box stores is metal clad, not armored cable. AC, & MC cables are solid wire which is not a good thing when vibration is present.
pattenp
Virginia - USA
Thanks all.
Yes and no. 28A X 1.25 = 35A. So #10 Romex is a no, max is 30A. If THHN then yes, max is 35A for #10 THHN.
And BX is no longer made. It has conductors with rubber insulation...Been replaced with AC...
pattenp
Virginia - USA
What is the basis for this multiplier calculation? In other words, what is it taking into account or compensating for?
It's a NEC requirement that conductors are to be sized at 125% of the motor full load current rating. The 125% is also a requirement for any circuit supplying continuous loads. It's a safety margin so not to overload circuits.
I
iceman510
Understand. Thank you.
I have THHN for the connection from switch to compressor. I will have to check the size/type of the wiring from subpanel to switch.