compressor jbox or disconnect question
shannonw
Florida
Hey all,
i'm relocating my compressor yet again. Right now it's hard wired from the panel. Where i'm putting it i need to run conduit down a wall. My question is currently there is a square d pressure switch (no manual switch) on the compressor. Should i just run a junction box at the end of the conduit to the compressor or put a disconnect there?
it's all in line of sight of the panel, i'm just not sure if technically the disconnect may be better to turn on/off vs the breaker, i seem to recall reading on here a few times using the breaker is not recommended especially if it's under load.
C96
Put in the disconnect switch, make sure it is the correct rating for your compressor. If your compressor is controlled via a mag starter, you can wire a switch in series with the coil on the control relay.
teamextreme
Lakewood, CO
Code says it has to have a disconnect switch within 50ft and within sight. If your breaker meets these 2 criteria, then it's fine without a local disconnect switch. Is it better to have one? Maybe, maybe not. In 20-some years of having a compressor I can't think of once I needed to kill power that flipping the pressure switch didn't accomplish what I needed. So you have to ask yourself if the added expense that exceeds code requirements is really necessary.
shannonw
Florida
thanks for input, the square d pressure switch doesn't have a 'manual' switch, nor is it a mag starter. I just use the breaker though, it's rare i turn it off under load. but i do turn it on by the breaker.
i'm in sight , only 15 feet away so that's not an issue code wise.
Mainly need a jbox or disconnect just to have something the conduit can fit in instead of just running a romex through a flex cable hanging out of drywall. I'd do a jbox to clean that up but if there's an advantage to a disconnect may do that.
Either way seems a 10hp disconnect only looks like a few bucks for the correct hp and amps (5hp 21 amp compressor motor)
b-body-bob
Almost Heaven
When I upgraded compressors I used a square D disconnect from either Lowe's or Home Depot, with 30A slow-blow fuses. It wasn't cheap but it wasn't real expensive either. I feel better turning that off instead of the breaker, since the disconnect is meant to be turned off and on but a breaker really isn't.
shannonw
Florida
b-body-bob, Sounds like a good idea, i think that's what i recall reading on here and is the general suggestion vs a breaker. Given the cost isn't much i'll just wire a disconnect in there, couple extra bucks for some additional peace of mind.
Norcal
Use a pullout A/C disconnect, they can be bought under $10, and come in 3 flavors, 30A & 60A fusible & 60A non fusible.