Compressor mag starter question

dmaxfireman

Well-known member
Joined
May 12, 2019
Messages
190
Location
CT
I am putting together a Frankenstein compressor with a Leeson 5hp (20.8FLA) single phase motor. The motor has a thermal overload reset on it. Read plenty of threads recommending a mag starter over only running a pressure switch.

Can I mount a 2 pole contactor in a junction box and have it function the same as a magnetic motor starter? Idea would be 1/3 - 1/2 the cost of a mag starter.

Is there any reason to go with a 120v vs 240v coil?
 
Last edited:
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
I am putting together a Frankenstein compressor with a Leeson 5hp (20.8FLA) single phase motor. The motor has a thermal overload reset on it. Read plenty of threads recommending a mag starter over only running a pressure switch.

Can I mount a 2 pole contactor in a junction box and have it function the same as a magnetic motor starter? Idea would be 1/3 - 1/2 the cost of a mag starter.

Is there any reason to go with a 120v vs 240v coil?

Is the motor supplied with factory overload protection? If yes then a contactor would be OK, if not then a magnetic starter should be used, a contactor that is UL recognized, is not kosher to use though, it needs to be listed by a NTRL, Nationally Recognized Testing Laboratory such as UL, CSA, or ETL, to name a few. a 240V coil means a neutral or control transformer will not be needed like it would with a 120V coil.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,016
Location
Modesto, CA
Is the motor supplied with factory overload protection? If yes then a contactor would be OK, if not then a magnetic starter should be used, a contactor that is UL recognized, is not kosher to use though, it needs to be listed by a NTRL, Nationally Recognized Testing Laboratory such as UL, CSA, or ETL, to name a few. a 240V coil means a neutral or control transformer will not be needed like it would with a 120V coil.

second sentence says motor has a thermal overload reset on it
 
OP
D

dmaxfireman

Well-known member
Joined
May 12, 2019
Messages
190
Location
CT
Is the motor supplied with factory overload protection? If yes then a contactor would be OK, if not then a magnetic starter should be used, a contactor that is UL recognized, is not kosher to use though, it needs to be listed by a NTRL, Nationally Recognized Testing Laboratory such as UL, CSA, or ETL, to name a few. a 240V coil means a neutral or control transformer will not be needed like it would with a 120V coil.

Doesn't UL fall under NRTL? Why wouldn't a UL listed contactor be acceptable?
 
Last edited:
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
Doesn't UL fall under NRTL? Why wouldn't a UL listed contactor be acceptable?

I said a UL Recognized contactor they are a recognized component of UL listed equipment and can be used replace one on listed equipment but unless want to pay to have it listed by a NTRL, better to buy a listed contactor, one will have a UL logo and the other will have a U with a backwards R on it. They are not the same.
 