396foxRN
Well-known member
I have the 7.5hp single phase baldor/quincy compressor setup now, and ready to wire it up. I am uncertain as to what all I need. I have a Schneider GV3P50 37-50A motor starter/circuit breaker (first two pics), a pressure switch, and an on/off switch. I figure that I need the LC1D50A contactor (pics 3 & 4) to go with it, but am not really sure what else from the catalog pics below (last 2 pics) that I need or don't need. Also, am unsure on which of the available coils to get with the contactor, as they seem to be offered in 12,24,115,230v setups.
So far, I have a 60A breaker, with 6ga wire into a 60A a/c disconnect and hardwired into the motor starter box.
Any help is greatly appreciated. Thanks!
So far, I have a 60A breaker, with 6ga wire into a 60A a/c disconnect and hardwired into the motor starter box.
Any help is greatly appreciated. Thanks!
The ONLY places where all poles need to be switched are at the disconnect and circuit breaker