Compressor Motor Suggestion

bfr57

Well-known member
Joined
May 31, 2013
Messages
133
I have a box store CH 80 gallon compressor that's 10+ YO. I use it pretty hard sand blasting and running air tools so it goes into a continuous run mode often. I replaced the pump 4 years ago with an Eaton double stage after the stock CH locked up. Now the motor is giving me problems; blew a start capacitor and after replacing that it's popping the thermal switch after about a 30 minute continuous run. It's a typical 5HP Emerson 56T frame running 3450 RPM. I know these motors are cheap and designed for light duty and not continuous. So, shopping for a replacement. Doesn't necessarily need to be a 56T frame or spin at 3450 since I can drill new holes if needed. Would actually prefer to slow it down a bit. Any suggestions?
 
To avoid these ads, REGISTER NOW!

Jswain

Well-known member
Joined
Apr 26, 2013
Messages
2,455
Location
Calgary, AB
Agree with the recommendation on a 1750rpm Baldor. Just make a note too as it probably won't have a thermal overload button in it so you will want to get a magnetic starter as well which is not a bad thing if you are a heavy user
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
13,996
Location
West central Indiana
A 1750 rpm WEG would be just as good as a baldor. A leeson is the best and sometimes you can find one for the same price. They are going to be a 182 or 184 frame size probably. If you look at your current motor plate, the FLA are probably not ~21 amps and there fore is not a true 5hp motor.
 
OP
B

bfr57

Well-known member
Joined
May 31, 2013
Messages
133
Yes sir, Tool Tyrant, and had to be dual-belted also. Will have to do it again going to a 1750 rpm!
 
OP
B

bfr57

Well-known member
Joined
May 31, 2013
Messages
133
Thanks for the suggestions. Will start shopping around. I'm sure the motor will only get worse as our temps are heading for 100 here in southern AZ!
 

Jswain

Well-known member
Joined
Apr 26, 2013
Messages
2,455
Location
Calgary, AB
If it's pretty dusty in that area you could try giving the motor a good blow through with an air hose, pull it out from the wall a bit more etc. A large 20" fan pointed at it helps cool it down pretty quick between cycles.
 
OP
B

bfr57

Well-known member
Joined
May 31, 2013
Messages
133
Thanks Jswain. I was thinking about a fan the other day. I have it outside in a enclosure that's well ventilated. I would have to pull a neutral line out to it to add a 110 VAC fan and maybe put a switch inside the garage. I also thought of adding a small light bulb tied into the pressure switch to let me know when it's running. At least my air cooling system is working with the aftercooler and air dryer! Not a drop of water anywhere.
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,724
Location
SE Michigan
If you had a 3450 (2 pole) and get a 1725/1750 (4 pole) you will need to re-sheave the motor.

Typically the compressor sheave has fan blades cast into it and that's not an easy one to change.

I recommend taperlock sheaves (SDS/QD) as they squeeze the shaft and won't loosen up over time. The taperlock bushing has to be sized to the motor shaft. 1-1/8" is common for 5hp IIRC.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO

Jlarson

Well-known member
Joined
Mar 27, 2015
Messages
738
Location
AZ
We put a lot of farm duty motors on compressors especially outdoor ones here. Usually Teco motors cause that's what I get from my usual supplier. TEFC, continuous duty, sealed bearings. Pretty common thing for us to do on smaller receps like that, along with putting on mag starter and new pressure switches.
 

redmondjp

Well-known member
Joined
Nov 25, 2014
Messages
2,318
Location
Redmond, WA
We put a lot of farm duty motors on compressors especially outdoor ones here. Usually Teco motors cause that's what I get from my usual supplier. TEFC, continuous duty, sealed bearings. Pretty common thing for us to do on smaller receps like that, along with putting on mag starter and new pressure switches.

Just one caution - Totatally-Enclosed, Fan-Cooled (TEFC) motors typically have a lower service factor (1.0 instead of 1.15 or 1.25), meaning that they are less tolerant of being overloaded. This is because it is more difficult to get the heat out of the motor windings on this type of motor.

For dirty/dusty conditions or where it may get wet, using this type of motor is fine, but in most cases, you are better off with a conventional motor design with open windings as it will run cooler which results in the motor lasting longer due to less rapid winding insulation breakdown.

Also look at how many starts per hour a motor is rated for - often it is a fairly low number, say 5 starts per hour. During starting, up to 10 times the running current can briefly pass through the windings, resulting in a great deal of heat building up in the windings. The limit on the number of starts per hour is to allow that heat to get out of the motor (which happens most quickly when the motor is running with the internal fan blowing air through the housing), thereby limiting winding temperatures to a safe limit.

All that to say that TEFC is not "better" in every situation. There are downsides to it that should be understood.
 

Jlarson

Well-known member
Joined
Mar 27, 2015
Messages
738
Location
AZ
That's why we use farm duty motors not just any old motor off the shelf.

No derated SF like some.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Not really helpful, but related and semi-funny. I had a guy tell me once if the motor is running the pump too fast, get a longer belt and remount the motor further away from the pump. He was adamant that since the longer belt had a larger diameter, it would turn the pump slower. Yes, he was an engineer...

Tommy
 

The Tool Tyrant

ALLIANCE MEMBER
Joined
Dec 19, 2011
Messages
2,182
Location
Bonita, Ca. (San Diego)
Not really helpful, but related and semi-funny. I had a guy tell me once if the motor is running the pump too fast, get a longer belt and remount the motor further away from the pump. He was adamant that since the longer belt had a larger diameter, it would turn the pump slower. Yes, he was an engineer...

Tommy

Railway or sanitation?:willy_nil
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,912
Location
Coronado, CA
Cheap prices in Electric Motors and Paint do not indicate Bargains.

Just as Cheaply made Paint should be avoided, the "Savings" on a Cheaply Made Motor may go up in SMOKE.
 

redmondjp

Well-known member
Joined
Nov 25, 2014
Messages
2,318
Location
Redmond, WA
It hasn't been resolved on this thread yet as to whether the replacement pump was set up properly to match the available horsepower of the (now-failed) motor. That should be verified first, else the replacement motor may also fail in a similar manner.

Cautionary tip: motors still work when overloaded, until the overload protection (if any) kicks in, or until they fail. This is why the above step should not be overlooked.

If the existing pump needs an extra half HP at the speed and pressure that it is operating at, then the motor will try to deliver that extra power, even if it above its nameplate rating. This is a very common issue on frankencompressors.
 