I have a 5hp compressor and the thermal overload trips on the mag starter after 10-15min of run time. After reset, it seems to run fine.
The motor is pulling 30-32A. I checked this since I installed a new replacement pump. Yes it is spinning at correct RPM. Also verified the current draw with pump MFG and he said it's normal.
I also have this unit hooked up with 30A breaker and #10 wire and it has never tripped the breaker.
The mag starter is a Furnas and may be original to the unit dated 89'. I've read that heaters get weak over time?