I searched and found conflicting information, so I figured I would ask again. My situation is that I have a Champion 5 HP compressor that I am converting to single phase with a Baldor 5 HP motor. The nameplate full load amperage is 23 amps.
Going by the method described in other posts:
Full load amps (table, 230V): 28
125% for conductor sizing: 35
From this information, I come up with #10 THHN conductors in conduit (EMT), and at least a 40 amp breaker. Sound right?
When using THHN, I am allowed to use the 90 deg C column in Table 310-16, correct?
Also, is a #12 THHN ground acceptable for this scenario?