Hi all,

Need an advice on running a dedicated line for the compressor. The motor on the compressor is 5hp 230v 20.8A full load. The run is going to be about 40 feet through conduit. Am I safe using #12 copper wire with 30A breaker on the sub-panel?

Please and thank you!
 
To avoid these ads, REGISTER NOW!

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
But he was right about the #10. 5 HP @ 240 is more like 16a calculated but the name plate is the ruler.
 
OP
T

tiggi

Well-known member
Joined
Sep 12, 2014
Messages
253
Location
USA
Yea i was going by the nameplate. Thanks for the info guys.
 
To avoid these ads, REGISTER NOW!
OP
T

tiggi

Well-known member
Joined
Sep 12, 2014
Messages
253
Location
USA
Also is there a difference if I use NM-b or THHN wire?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Also is there a difference if I use NM-b or THHN wire?

Yes. The temperature rating is different. NM-b has to be sized @ 60C whereas THHN can be sized @ 75C. So for the compressor circuit #10 NM-b is 30 amps and #10 THHN is 35 amps.

This does not apply for general branch circuits because small conductor rules kick in and #10 Cu is limited to 30 amps.
 
Last edited:

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
So would it be ok if I use #12 THHN?

Do us a favor, if you're going to start a thread asking how to wire a 5HP compressor despite the fact there are many threads that have been already answered with the same question, at least read the responses you get.

Where did anyone say recommend anything less than #10?

Just so we're clear, #12 is NOT ok!

Jeez, some people are so helpless.
 