The wife just gave me an early Christmas present! A Beacon Morris separated combustion heater!
I want to get it mounted and vented to my HVAC guy can come connect gas.
After reading through the instructions for the separated combustion venting it leaves me confused. It states that you must use "one piece" of B-Vent through the concentric box up to the vent cap. The longest B-Vent I have ever seen is 5 ft. Does two pieces properly connect and caulked count as one?
If not how are you guys making this work, how do you meet the "one piece" requirement, the 2ft above anything withing 10ft requirement, and the snowfall requirement (which from what I can find is 3ft for MI)? I have a 4/12 roof and I planned to put the concentric box in the garage not attic. In order to do this I would need a b vent at least 7ft long.
Any thoughts?
I want to get it mounted and vented to my HVAC guy can come connect gas.
After reading through the instructions for the separated combustion venting it leaves me confused. It states that you must use "one piece" of B-Vent through the concentric box up to the vent cap. The longest B-Vent I have ever seen is 5 ft. Does two pieces properly connect and caulked count as one?
If not how are you guys making this work, how do you meet the "one piece" requirement, the 2ft above anything withing 10ft requirement, and the snowfall requirement (which from what I can find is 3ft for MI)? I have a 4/12 roof and I planned to put the concentric box in the garage not attic. In order to do this I would need a b vent at least 7ft long.