Condenser Wire & breaker size

jacks2000

Well-known member
Joined
Oct 9, 2012
Messages
54
Location
Kansas
What size wire and breaker should I use for a Nordyne 4 ton 16 SEER condenser? Manual lists Total amps as 23.7 and minimum circuit ampacity as 29.0. Distance from breaker panel to disconnect is 35'.
For my 5 ton it's total amps 31.4, Minimum ampacity is 38.6. Distance will be about 60'
Thanks
Jack
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
Wire is sized by minimum, breaker is sized by the maximum.

Now does the manual call for different size for an HACR breaker vs. time delay fuse?
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
A lot of times manuals are out of date. What does the nameplate on the unit show?
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I always go to http://www.cerrowire.com/ampacity-charts and make sure the wire is rated to more than my expected usage, if possible the bigger the wire the better. Breakers/fuses can NEVER be rated above the maximum ampacity of the smallest wire connected to them.
This is fine for people who would rather over-do and over-spend without knowing what is code required and code legal.

The topic of this thread is an air-con condensor. That chart and link you provided does NOT apply.
It is quite possible that the 29MCA unit can be wired with #10 and put on a 40 or 50A breaker.
The 39MCA unit can/should use #8cu and a 50A breaker.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
With A/C equipment you wire to the minimum, use the maximum allowed fuse/ circuit breaker, according to what the data plate says, you do not need to size the conductors at 125% as the manufacturer has already done so.
 
OP
J

jacks2000

Well-known member
Joined
Oct 9, 2012
Messages
54
Location
Kansas
I can't check the plate because the condenser won't be delivered for a couple months. We need to run the wire now so I got the info from downloading the installation manual from Nordyne's website. I looks like I should run #10 wire and a 40 or 50 breaker for the 4 ton. I'll run the #8 and a 50A breaker for the 5 ton.
Thanks for everyone's replies.
 