I’m filling out the permit application to add a hard-wired Level 2 EV charger and need to decide whether a trench is necessary.

Relevant info: 2017 NEC code cycle, Pennsylvania USA, 40 amp branch circuit on 240v split phase residential power, fed from a sub panel in the garage. I will add an AC disconnect even though it’s not required per 625.23.

I can’t find any code prohibiting the use of schedule 80 PVC (not sch40 because of physical damage) mounted along the back side of a curb / wall at the back of a driveway, as shown in my cartoon below. I could bury RMC at 6” per table 300.5 if I must, but that feels unnecessary.

Can anyone think of a violation this would cause?

642E13BA-6611-4D04-978B-D023CC734186.jpeg
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,617
Location
Richmond, VA
i can't think about why that wouldn't be ok. i think i'd use an expansion joint on the horizontal run

that handrail top tube looks just like conduit though... ;)
 
To avoid these ads, REGISTER NOW!

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,969
Location
Coronado, CA
Rigid Conduit handrail? going to be interesting to see how the conductors enter the conduit and then pass through to the connection box for the charger.
 