Conduit and derating
Mike Honcho
couldnt seem to find what i was looking for searching, so heres my question.
can i run one 1/2 emt with 2 hots, 2 neutrals, and 2 grounds 12 ga thhn, and still be good for 20 amps? or does derating come into play at that point.
and my second question is can i use the boxes for the first circuit as a pass through for the second circuit? reason being is i want to run each wall seperate, but trying to run only one conduit.
thanks.
alfredeneuman
Fullerton, CA
You only need 1 grounding conductor, not 2, and if the circuits are fed from different the 2 legs (both A & B) you only need 1 neutral.
That being said, as many as (9) THHN/THWN can be run in a conduit without having to derate/upsize, so you're good to go there.
2nd question:
It's perfectly acceptable to run multiple circuits through the boxes, as long as you are mindful of the box fill limits.
Mike Honcho
2nd question:
just what i was looking for, i was aware of running, a mwbc, but having no knowledge good or bad, i was leaning away from them. i was also unaware 2 seperate circuits could share one ground.
i should be ok on box fill, i have 4 inch deep boxes with 1/2 raised covers.
thanks again!
2nd question:
Huh? 4 or more CCCs(current carrying conductors-hots and neutrals) in the same raceway must be derated.
In the OPs case, he would be fine with 4 #12s because 90* c ampacity is 30a x 80% = 24a.
And if he went with a MWBC, then none of this applies as it would only be 3 conductors...
Aceman
Eastern Oregon
I think Alfred was saying you can put 9- #12 THHN's in a pipe and still use a 20 amp breaker. After 9, derating starts cutting into the allowable ampacity pretty hard.
zmaxmotorsports
South of omaha
What are you running off these circuits,how far and how many bends between boxes?
Personally Id rather run 3/4" pipe than fight pulling 9 #12s through a piece of 1/2",you can always drop it down to 1/2" as you drop circuits off along the way.
And remember if you run a ground wire through the pipe it should be bonded in each box.:)
Mike Honcho
i am also staying away from mwbc because i have enough single pole breakers.
so if am understanding alfred right, i can run 2 hots, 2 neutrals, and only one ground? so 5 wires in total?
Mike Honcho
Something just dawned on me, would the fact that each circuit will start with a gfci outlet change the fact that they can share a ground?
sberry
Brethren, Michigan
No, the ground doesn't have anything to do with the operating part of the gfci. Its simply a bond or low impedance pathway back to the service neutral.