Hi Everyone,
So it is getting near the time for me to actually start the job of running electrical out to my detached garage. I have had several threads in the past and they have all been very helpful with many aspects of the project. Now I want to concentrate on the wire from the inside panel to the garage!
Based on recommendations, I am going to run 4/0 XHHW-2 Aluminum the 230ish feet to the garage.
Since I want to plan for the future, I am going to run 3 conduits from the panel to under the house - with only the garage one coming out at this time. One is 2.5" for the garage, the next is a 2" to support a possible pool on that side of the pool, and a 1.25" (or 1.5") for a new circuit to support the future screened in porch (lights, ceiling fan, TV). All three conduits will go into the crawlspace.
Look at the attached picture, "A" is for the garage, "B" is for the pool, and "C" is for the porch.
The plan is a junction box (in red) where I will step down the 4/0 wire to a smaller size (the Eaton CH2125 breaker accepts copper/aluminum wires of size 10 - 1/0-AWG).
Since I am not sure how much power standard pool equipment requires and a corresponding pool house with lights, TV and refrigerator, can I assume the worst and calculate using another 125A breaker?
The 12 gauge wire (UF) for the porch would just be a pass through.
So how big does this junction box have to be and what type? I tried doing some research and got lost with all the options/variances, etc.
My twin 200A panels are on the other side of the meter so I would go through the junction box and into a panel (cut drywall out on the inside to run conduit into existing panels)
The next question is how to get the three conduits around the corner and then under the house(to come out the other end). Do I stagger them at various depths? (Reference other pic) - top("C") at 18 inches, "A" at 22 inches and "B" at 24 inches? Is that acceptable for code?
I really only want to dig this area up once!
So it is getting near the time for me to actually start the job of running electrical out to my detached garage. I have had several threads in the past and they have all been very helpful with many aspects of the project. Now I want to concentrate on the wire from the inside panel to the garage!
Based on recommendations, I am going to run 4/0 XHHW-2 Aluminum the 230ish feet to the garage.
Since I want to plan for the future, I am going to run 3 conduits from the panel to under the house - with only the garage one coming out at this time. One is 2.5" for the garage, the next is a 2" to support a possible pool on that side of the pool, and a 1.25" (or 1.5") for a new circuit to support the future screened in porch (lights, ceiling fan, TV). All three conduits will go into the crawlspace.
Look at the attached picture, "A" is for the garage, "B" is for the pool, and "C" is for the porch.
The plan is a junction box (in red) where I will step down the 4/0 wire to a smaller size (the Eaton CH2125 breaker accepts copper/aluminum wires of size 10 - 1/0-AWG).
Since I am not sure how much power standard pool equipment requires and a corresponding pool house with lights, TV and refrigerator, can I assume the worst and calculate using another 125A breaker?
The 12 gauge wire (UF) for the porch would just be a pass through.
So how big does this junction box have to be and what type? I tried doing some research and got lost with all the options/variances, etc.
My twin 200A panels are on the other side of the meter so I would go through the junction box and into a panel (cut drywall out on the inside to run conduit into existing panels)
The next question is how to get the three conduits around the corner and then under the house(to come out the other end). Do I stagger them at various depths? (Reference other pic) - top("C") at 18 inches, "A" at 22 inches and "B" at 24 inches? Is that acceptable for code?
I really only want to dig this area up once!