conduit fill for SER cable?
Innovate1
I am planning to add a 50A RV receptacle and have AL 6-6-6 with 6 ground with OD of 0.717". Will be using Sch 40 conduit for protection from the attic down the wall to the receptacle. It fits loosely in 3/4 PVC conduit but not sure it meets code due to fill. I read someones opinion (not on this site) that since it isn't continuous conduit the 53% fill limit doesn't apply but not sure that's true.
Running the numbers with 3/4" sch 40 PVC it is 76% fill and with 1" it is 47% fill. Do I need 1" conduit or is 3/4 ok?
SER doesnt need to be in conduit unless its subject to damage. doesnt sound like your install would be. I would just skip the conduit, especially PVC, and just run the SER. if you must use conduit, individual conductors would be far cleaner and easier. Could use #8 cu THWN w/ a #10 green ground
I
Innovate1
I don't think #8 AL is good for 50A at 75C. You must have been considering copper.
Maybe SER on the wall of a garage would be considered NOT subject to damage - not sure about that one. Figured it would look better in conduit and I already have the wire. I am not running conduit the whole way and this way I don't need any junction boxes. Doing a bit more searching on this I think a 60% limit applies if the sleeves are 24" or less (mine are much longer) so technically I think 1" is required.
mike93lx
Richmond, VA
Afaik, the 60% fill only applies up to 24", as you noted. after that, I would assume that normal fill rules apply.
I'd just follow the normal fill rule especially since it's a short run. Guessing one 10' stick does it?
Bert_
NW Iowa
SER doesnt need to be in conduit unless its subject to damage. doesnt sound like your install would be. I would just skip the conduit, especially PVC, and just run the SER. if you must use conduit, individual conductors would be far cleaner and easier. Could use #8 THWN w/ a #10 green ground
Ser left exposed outside does not hold up well. I always sleeve exterior portions of a run and would recommend the same to anyone else.
I
Innovate1
Guess I wasn't clear that this is inside. Putting it just inside the OHD. That way I don't have to worry about weatherproof cover. It's running up the inside of a finished wall.
And yes on one 10' stick being enough.
mike93lx
Richmond, VA
SER (I guess actually SEU) running on the outside of a house is very common where I grew up in New england, including the house I used to own as well as my folks. Seemed to do ok. What issues have you encountered with it?
Bert_
NW Iowa
The outside coating gets brittle. Cracks if you even breathe on it.
sparky 1971
Central Iowa
We have a local amendment that all service entrance conductors have to be in metal conduit. Ain't running no SEU or SER on the outside walls around here. I just follow that train of thought no matter what jurisdiction I'm in.
I
Innovate1
And I don't meet 60% anyway. So 1" is it. Although I have seen people claim that raceways used for physical protection don't have fill limits I am guessing that is wrong.
mike93lx
Richmond, VA
The internet claims a lot of things. Like Nm can't go in conduit
I go back to the part about it only being a single stick. $10 for 3/4, $14 for 1, and $19 for 1-1/14. I'd be making my job as easy as possible at those prices