Conduit "fill" of a pull elbow

afazz

Well-known member
Joined
Nov 25, 2007
Messages
860
Location
Pittsburgh, PA
I have a 6-50 receptacle adjacent to my panel, shown in the attached picture. It's primarily for a welder (I know NEC allows smaller conductors for welders), but not technically a dedicated outlet. I used 6awg THHN because I had it laying around. Protected with a 50amp breaker.

The two 6awg hots and one 10awg ground doesn't quite feel right in the pull elbow - it's very tight. Is there a specific code that prohibits this? I'm within the fill limits of the 3/4 EMT and the box with the raised cover, but I couldn't find anything limiting the fill of a pull elbow.
 

Attachments

  • Image_20210307_092932.jpg
    Image_20210307_092932.jpg
    94.2 KB · Views: 82
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
The Pull elbow would have the same wire fill requirements as the EMT. You have not exceeded the fill limit, try pulling back on the wire a bit so they are not so tight.

EDIT - Since the EMT is 2 ft. long or less, it may be increased to a 60% fill, but the pulling elbow would still have a maximum 40% fill. It would not change anything with your installation, it still is code compliant.
 