I’ve run conduit throughout my garage. Made it perfect so it looks nice. Ran conduit to box above my two post lift and intended to use flexible metal conduit down to the box. But it looks like ****. Thinking of running conduit straight down to a box. Question is the post can move a little and wonder if I can mount hard lines or do I need some kind of flexible connector at the top of the post?


Sent from my iPhone using The Garage Journal mobile app
 
To avoid these ads, REGISTER NOW!

sreeb

Well-known member
Joined
Jul 29, 2009
Messages
460
Location
SoCal
I ran hard conduit.

It will flex some and neither your building nor your lift should move much.
 

rsanter

Well-known member
Joined
Dec 22, 2007
Messages
18,506
Location
visalia ca
How long will the drop be?
If it’s a couple feet or more long it will have plenty of flex in it
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
If you're lift is moving after being bolted to floor I'd say you've got bigger problems to worry about.



It’s not. Doesn’t mean it’s not required to have a flexible part. I’ve never tried to measure but I’d guess all move a little with a superduty on it. Especially at the top where I’m asking about


Sent from my iPhone using The Garage Journal mobile app
 

Ray-CA

Well-known member
Joined
Jan 6, 2007
Messages
3,451
Location
San Diego CA
Could you use a short length of flex conduit between the ceiling and the remainder of the conduit? Kinda like using a flex hose between the compressor and your hard pipes/

Ray
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I would run EMT down the lift column, but transition to flex to go between the wall and the lift column.
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
Could you use a short length of flex conduit between the ceiling and the remainder of the conduit? Kinda like using a flex hose between the compressor and your hard pipes/

Ray

If required this is what i would do. 90 down and then 6 inches or so of flex conduit then back to conduit.
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
I would run EMT down the lift column, but transition to flex to go between the wall and the lift column.

assume you meant between lift column and box. yes i don't think i have enough room to do a 90 down there so it will be flex of some sort.
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
Rigid is fine. The only thing is to estimate the amount of movement and then see if its going to damage the box where it attaches.

I would go flex from the ceiling box then connect that to the rigid on the hoist with ac to conduit fitting (no box).
 

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
You can also use the bends in conduit to your advantage. Think of making a "spring" out of the conduit (either with bends you already have to have or with additional strategically added bends).

EMT will be unhappy if you ask it to stretch/flex 3/4" along its length. It will be better able to absorb that much flexing through a series of bends.
 

crook038

Well-known member
Joined
Nov 3, 2010
Messages
113
Location
South Eastern MA
I used SOOW cord from the ceiling to the limit switch then down to the motor control. Simple and allows post flex(yes the post tops do move a small amount when lifting a vehicle.)
Sean
 

Attachments

  • 3195DD38-08AD-4925-B2E0-B82DC29F6435.jpg
    3195DD38-08AD-4925-B2E0-B82DC29F6435.jpg
    54.2 KB · Views: 159

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
^^^^^^^^^^^ :+1:
Flex needs to supported within 12" of each end, and every 4-1/2 feet in between.

Lifts, elevators, and cranes can be, by the NEC, hardwired with cord and only require strain relief connectors at the terminations.
 
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
What I did - no box in the attic, just a bushing and ran the NMC down the pipe.

LiftPower.jpg
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,585
Location
BC
If you're worried about the EMT couplings/connectors pulling apart as it flexes, run that stretch with a bond wire to maintain the ground path.
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
If you're worried about the EMT couplings/connectors pulling apart as it flexes, run that stretch with a bond wire to maintain the ground path.



Not overly worried about grounding. More about it separating then pinching a wire going back together. Very low risk but I’m guessing the inspector will question it


Sent from my iPhone using The Garage Journal mobile app
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,585
Location
BC
If conduits are separating you REALLY want to be worried about grounding. The ground path is contingent on all the connectors staying tight. Running the extra conductor would be a good choice IMO. Also sets you up well in case you need to use a piece of flex conduit. I'd probably use something like a length of unistrut off the lift column to get closer to the wall or ceiling you're feeding from.
 
To avoid these ads, REGISTER NOW!
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
If conduits are separating you REALLY want to be worried about grounding. The ground path is contingent on all the connectors staying tight. Running the extra conductor would be a good choice IMO. Also sets you up well in case you need to use a piece of flex conduit. I'd probably use something like a length of unistrut off the lift column to get closer to the wall or ceiling you're feeding from.



Wasn’t worried as I believe the whole lift is grounded. I will have to look at the motor again.


Sent from my iPhone using Tapatalk
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,968
Location
Central Iowa
I have hooked up about eight lifts. On each one, I turned an emt 90 down from the ceiling, then transitioned to about a foot or so of flex, then back to emt down to the lift control. The short piece of flex should be enough to take up any vibrations.
 

acnsx1

New member
Joined
Jan 1, 2020
Messages
1
Location
connecticut
just had my lift installed and ran flexible conduit from a box in ceiling to a twist lock outlet. motor lead has a matching twist lock plug. looks good. i'm not ocd :)
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
I have hooked up about eight lifts. On each one, I turned an emt 90 down from the ceiling, then transitioned to about a foot or so of flex, then back to emt down to the lift control. The short piece of flex should be enough to take up any vibrations.



What fittings go from flex to solid? Do I use a connector for a box and just not use the lock nut? Threads looked different then specific flex connector that screws into flex conduit


Sent from my iPhone using The Garage Journal mobile app
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,968
Location
Central Iowa
What fittings go from flex to solid? Do I use a connector for a box and just not use the lock nut? Threads looked different then specific flex connector that screws
Sent from my iPhone using The Garage Journal mobile app

There are fittings that make the emt to flex transition, but I have never used them. I use an emt connector and a flex connector screwed into opposite ends of a rigid coupling.
 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
I used the gray pvc conduit on my old 2 post lift. It can flex more than metal so I did not use any flex section between the ceiling box and the top of the post. I was going to the motor not an outlet so I used the gray pvc flex to curve over to a right angle fitting going into the motor.
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
There are fittings that make the emt to flex transition, but I have never used them. I use an emt connector and a flex connector screwed into opposite ends of a rigid coupling.



Never in a dozen years would I have thought of that. If it gets out of single digits I’m going to give this a try

Edit
For any other idiots....threaded rigid coupling. Off to the store...


Sent from my iPhone using The Garage Journal mobile app
 
Last edited:
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
A few trips to the store and pretty much have it. Need to find a better box for my emergency stop switch but I have the hard lines in place.
Thanks for all your help.
a2b7c5c1c458e428a96b1113fc14669f.jpg
50b13718d3e246ec11ac711b116029c0.jpg


Sent from my iPhone using The Garage Journal mobile app
 

Attachments

  • a2b7c5c1c458e428a96b1113fc14669f.jpg
    a2b7c5c1c458e428a96b1113fc14669f.jpg
    146.6 KB · Views: 19
  • 50b13718d3e246ec11ac711b116029c0.jpg
    50b13718d3e246ec11ac711b116029c0.jpg
    119.7 KB · Views: 32

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
That looks pretty good.

What kind of lift is it that routes all the hoses exposed on the outside?
 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
All lifts run the hoses on the outside of the posts.

My Atlas did not, but was a baseplate. My Bendpak does not, but is a 4 post. So maybe it is just 2 post top plate lifts that run hoses on the outside of the columns.
 

Super Mech

Well-known member
Joined
Feb 19, 2011
Messages
1,806
Location
Bronx,NY
I have three lifts and they all have rigid piping. No problems in 8 years in this shop. In the old shop they had rubber cords from a box on the ceiling. I hated the way it looked but that’s how I got the shop.
 