75gmck25
I have a detached garage that will require about 45 feet of buried cable to run electric for a sub-panel, and another run for low voltage cat 6 and coax lines. I plan to use a 60 amp breaker for the connection to my Square D QO main panel, since that seems to be sufficient for what I need. I could also use a 90 amp breaker, but that seems to up the breaker price significantly.
My power needs for the garage are moderate. I have a window A/C, small 120 volt compressor, lights, grinder, table saw, etc., and may buy a small welder in the near future. The only reason I can think of for needing as much as 90 amps is if I add an EV charger in the garage, which is not likely.
I have already run aluminum SER 2-2-2-4 from the main panel to the inside wall of the house nearest the garage, and now need to transition to MHF or THWN for the 45 foot underground run in conduit from the house to the garage.
I need to decide what cable to run underground, and what conduit size I need. Aluminum MHF in 2-2-4-6 and 2-2-2-4 are available by the foot for a reasonable price, or I could run separate THWN wire. However aluminum MHF seems likes the easiest and cheapest choice.
If I run MHF, is 2" conduit large enough to easily pull about 50 feet? It will come out of the house wall, turn 90 degrees down, then another 90 to go straight out into the trench, and then two more 90's to come out of the trench and into the side of the garage. I will have a another junction box there to transition from MHF back to SER, since its my understanding that I can't run MHF within the structure.
For the low voltage run of a coax cable and two Cat 6 cables, what would you recommend for conduit size? It seems like 1 1/2" is large enough, but I'm not sure how well multiple low voltages cable will pull (do they bind on each other?).
Thanks,
Bruce
Thanks,
Bruce