anthonyjorgensen
Member
When I poured the footings for the shop I'm building I ran 1.5" conduit up through the wall. Originally I was planning on running 4 AWG ACWU90 through it to the panel. I'm only able to run a 60A service based on the current panel loads that I have on the main in the house. Now, I'm thinking that I'd like to run 1 AWG in case I ever upgrade the service to the house that way I could have 100A to the shop. Will I be able to pull 1 AWG ACWU90 through 1.5" conduit? There's only 10' of it with a 90 degree around half way, the rest of the cable is going to be direct buried.