Installing 2-2-2-4 SER cable between house and detached garage. I assuming the SER is not direct bury, so what is the minumum NEC size allows using gray PVC conduit for this cable. I will have a LB at the house and garage.
 
To avoid these ads, REGISTER NOW!

matt151617

Well-known member
Joined
Dec 17, 2011
Messages
488
Location
New Jersey
SER is not allowed underground/in conduit. You need mobile home feeder. 1 1/2" conduit would work but 2" would be much easier to pull through.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Hopefully you are just using the wrong term. If the cable you have is SER it should look like the picture below. If it is SER, it cannot be used below ground in conduit.

SER
032886584596lg.jpg


This can be used underground in conduit.
URD/ Mobile Home Feeder
145939_300.jpg
 