Going to be pulling about 400 feet of 2/0-2/0-2/0-1 through conduit with 3 or 4 45* sweeps. Was thinking of using 2" or would 3" really make things any easier?
What type of wire is this? AL MHF?
Going to be pulling about 400 feet of 2/0-2/0-2/0-1 through conduit with 3 or 4 45* sweeps. Was thinking of using 2" or would 3" really make things any easier?
AL URD Quadruplex. 1.316" outside diameter
pattenp Re: conduit size
--------------------------------------------------------------------------------
Do you plan on bringing the URD into the structure? If so, it's not allowed inside. Most URD is only rated USE-2 and has to be terminated outside of the structure. If the wire also carries a rating of RHH/RHW-2 then it can be run inside.
Karl, just out of curiosity, on your 4 wire URD, was it dual rated, where it can be ran inside the structure as PattenP has stated above
Does the neutral conductor have a white stripe or yellow stripe for identification?
The odds are if the wire is labeled as URD Quadruplex the neutral is yellow striped and three phase conductors are just black and the cable is only rated as USE-2.
Oh, OK. The reason I asked, we had a lengthy conversation about this at the supply house (several occasions) (I started posting this in another thread, but deleted it?)
Supply house guy says URD has a 6' rule, it has to be terminated within 6' of entering building (Never heard that and I dont think it exsists) he ends up calling manufacturer, maunufacturer rep states that URD with yellow stripe neutral cannot enter building, URD with white stripe neutral is dual rated and can enter building. This is a smaller supply house, they do not carry MHF, it is URD or XHHW on the alum. side
I just wanted to confirm the above info?
I have never used MHF, does it have the same insulation rating as URD
or are they the same as one?
Anyway, glad you got it pulled in Karl, 400' pull can be a bear. I am in the 4th week of waiting for the power company to tie my barn in, I was told we are waiting for a traffic permit to shut one lane down?
I've never seen white striped URD, only yellow.
URD cable is considered to be USE-2 cable by the Code.
338.12 Uses Not Permitted
(B) Underground Service-Entrance Cable.
Underground service-entrance cable (USE) shall not be used under the following conditions or in the following locations:
(1) For interior wiring