It's getting late and I have been working around the clock but I must be going cross eyed.
I am planning to run 4x#2 copper wire to my garage and I am planning to use 1 1/2" pvc schedule 40.
Here's were the confusion starts, according to the NEC 2008 book table c.10 for the maximum number of conductors in a 1 1/2" pvc using thwn#2 wire is 5
When I use the calculator for the cross section - 4 x 9.754mm = 39.016mm & the nominal internal diameter for 1 1/2" pvc is 40.4mm, how is there room for the 5th conductor?
So I guess my question after searching ALL the pages of this section and finding nothing solid then taking the gaint leap of trying to understand the NEC book, is, will 4 #2 copper wire fit in the conduit?
The builders used a 1 1/2" sweep in the foundation and I will have to chip it out if I have to use 2", a huge pain in the behind and not something I want to do.
Time to go to bed.