I just asked an electrician what size wire I needed for 200 amp and he told me. Then I ran a 125amp breaker on house panel. Figured if that pops or the main 200amp breaker feeding house pops I'll upgrade entire thing to bigger panel. So far no problems with the following
Qty 2. 5 ton ac units. Mig welder. Cnc plasma cutter. 2 2 post lifts. 10hp air compressor. 10hp rotary phase converter for mill and iron worker. Lots of equipment and 2 people working and no issues yet.

So based on TTMotorsports usage - looking way more than mine - I think I will be fine with 125A rated wire. (This will be aluminum - copper is too much $$$)
I think I need 2" conduit for that, correct? What wire size would that be?
IF I were to go with 2.5" conduit for the run, can I support 200A (aluminum wire) in that conduit? Thought being that a) it will be an easier pull for the 125A rated wire and b) god forbid I ever never more, I don't have to dig!! :)

Thanks!
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
So based on TTMotorsports usage - looking way more than mine - I think I will be fine with 125A rated wire. (This will be aluminum - copper is too much $$$)
I think I need 2" conduit for that, correct? What wire size would that be?

4/0 Al for 125A. 2" is the "correct" size conduit but 2 1/2" will pull a lot easier.

One other thing to check before you run pipe is whether your 125A breaker lugs will accept 4/0. You may need a box near your main panel to splice down to a size the breaker will accept.

IF I were to go with 2.5" conduit for the run, can I support 200A (aluminum wire) in that conduit? Thought being that a) it will be an easier pull for the 125A rated wire and b) god forbid I ever never more, I don't have to dig!! :)

Again 2 1/2" is correct for 350MCM but 3" would be better. And 350 could be a problem with lug sizes in both panels. Working with wire that large in residential panels wouldn't be easy even if it fit the lugs.....................

Your other option for a 200A upgrade would be 4/0 copper. Wire would cost more but would be easier than trying to deal with 350 Al.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,473
Location
Richmond, VA
4/0 Al for 125A. 2" is the "correct" size conduit but 2 1/2" will pull a lot easier.

One other thing to check before you run pipe is whether your 125A breaker lugs will accept 4/0. You may need a box near your main panel to splice down to a size the breaker will accept.



Again 2 1/2" is correct for 350MCM but 3" would be better. And 350 could be a problem with lug sizes in both panels. Working with wire that large in residential panels wouldn't be easy even if it fit the lugs.....................

Your other option for a 200A upgrade would be 4/0 copper. Wire would cost more but would be easier than trying to deal with 350 Al.

Ok - so 2.5" for the aluminum wire for 125A. If I need more power, I should switch to copper to keep size down - can 4/0 copper be run for that distance in the 2.5" conduit? (My thought is if I need 200A, I need to **** it up and do the copper - if I need that kind of juice, apparently I have $$$) :)

Oh - and I do plan on having a box near my house panel that I can do a splice. I assume I would need one on both ends then?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,417
Location
Richmond, VA
Ok - so 2.5" for the aluminum wire for 125A. If I need more power, I should switch to copper to keep size down - can 4/0 copper be run for that distance in the 2.5" conduit? (My thought is if I need 200A, I need to **** it up and do the copper - if I need that kind of juice, apparently I have $$$) :)

Oh - and I do plan on having a box near my house panel that I can do a splice. I assume I would need one on both ends then?

You only need a splice box if you have to change size or wire type.

The box size is impacted by the conduit size. Bigger the pipe, bigger the box.

You could have that box indoors if the wire is rated for indoor use. Xhhw would cover that.

125A is a ton of power. My entire house is 100a....electric dryer, two fridges, a freezer, well, 2 ton a/c, a furnace, lights, outlets, plus a welder and many power tools in the attached garage.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,584
Location
BC
125A is a ton of power. My entire house is 100a....electric dryer, two fridges, a freezer, well, 2 ton a/c, a furnace, lights, outlets, plus a welder and many power tools in the attached garage.

Similar here. 100A goes a long ways.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,473
Location
Richmond, VA
The plan is to go with 125A wire - that is the largest breaker that fits in my existing 200A panel. Would 4/0 wire connect to the breaker or am I looking at a splice box either way?
The next question is 2" vs 2.5" conduit. I am willing to spend the little extra for the larger if it makes the pull easier and could allow for an upgrade in wire....
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
Ok - so 2.5" for the aluminum wire for 125A. If I need more power, I should switch to copper to keep size down - can 4/0 copper be run for that distance in the 2.5" conduit? (My thought is if I need 200A, I need to **** it up and do the copper - if I need that kind of juice, apparently I have $$$) :)

4/0 copper should be a drop in replacement for the 4/0 aluminum. And yeah if you can afford that much power you can afford copper:lol_hitti

Oh - and I do plan on having a box near my house panel that I can do a splice. I assume I would need one on both ends then?

I guess you're going to put a 200A panel in the shop right away. That should accept 4/0 no problem so you'd only need to splice that end if you need to change from outdoor to indoor wire like Mike mentioned. It's unlikely you'll need to do that since you're using conduit.

The plan is to go with 125A wire - that is the largest breaker that fits in my existing 200A panel. Would 4/0 wire connect to the breaker or am I looking at a splice box either way?

You'll need to look up the specs for that particular breaker. IIRC Square D are 2/0 max but yours may be different.............
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,417
Location
Richmond, VA
And don't trim away some of the strands to make it fit.


No question 2.5" will make it easier, of course it would. As would 3".

Go as big as you want to pay for and look at. I know I wouldn't want a huge conduit on the side of my house.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,473
Location
Richmond, VA
And don't trim away some of the strands to make it fit.


No question 2.5" will make it easier, of course it would. As would 3".

Go as big as you want to pay for and look at. I know I wouldn't want a huge conduit on the side of my house.

On the garage the conduit is going up inside the block wall. The house side will be next to the large conduit feeding the house from the poco. Visually already exposed so what's another pipe. :)
 

grumpyvette

New member
Joined
Oct 1, 2019
Messages
3
Location
mid fla
check local building codes ,
many areas require the conduit to be 2" PVC and at least 24" below ground surface
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,417
Location
Richmond, VA
check local building codes ,
many areas require the conduit to be 2" PVC and at least 24" below ground surface

Why does that matter? There is no discussion on going below 2"

Besides, never heard that requirement, which really doesn't make sense anyway. Any proof?
 

rjcnaples

Member
Joined
Sep 23, 2018
Messages
17
Location
Florida
At 200+ feet and let’s assume (2) 90’s sweeps to get into and out of ground, and you can bow the run so there are not any more sweeps in it. I would use 2” pvc. (3) 4/0 AL, (1)#6 AL will fit and pull through it. You stated that a 125 amp is what you wanted originally. The 4/0 AL will carry up to 200 Amps. But at the distance you stated voltage drop will be no issue. This setup basically covers what you want and gives you the ability to upsize in the future easily.


Sent from my iPhone using Tapatalk
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,417
Location
Richmond, VA
At 200+ feet and let’s assume (2) 90’s sweeps to get into and out of ground, and you can bow the run so there are not any more sweeps in it. I would use 2” pvc. (3) 4/0 AL, (1)#6 AL will fit and pull through it. You stated that a 125 amp is what you wanted originally. The 4/0 AL will carry up to 200 Amps. But at the distance you stated voltage drop will be no issue. This setup basically covers what you want and gives you the ability to upsize in the future easily.


Sent from my iPhone using Tapatalk

4/0 AL is not good for 200a except in a service entrance application (feeding an entire residential structure) or when looking at a 90*C column, neither of which apply here.

In this application, 180A is best-case before considering voltage drop.
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,473
Location
Richmond, VA
So I had a quick call with my local inspector and told him I was running 2.5" conduit and he was fine with that and I mentioned going with 4/0 aluminum and he said if I am running off a 125A in my house panel that 2/0 is fine. He mentioned something about "80% of the breaker", "save some money", etc. He also said to use XHHW wire......
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,417
Location
Richmond, VA
So I had a quick call with my local inspector and told him I was running 2.5" conduit and he was fine with that and I mentioned going with 4/0 aluminum and he said if I am running off a 125A in my house panel that 2/0 is fine. He mentioned something about "80% of the breaker", "save some money", etc. He also said to use XHHW wire......

XHHW is fine, that's right.

Follow code and calculations, not the inspector's opinion.

If you want 125a,at an acceptable voltage drop, 4/0 is the answer. If you really don't need 125a,then downsize.

2/0 looks fine at 100a
 
Last edited:

rjcnaples

Member
Joined
Sep 23, 2018
Messages
17
Location
Florida
Just so you know. Most thermal- magnetic breakers. ( the type most residential panels use). Should be able when working properly carry 80% of the amps they are rated for continuously. They can also take amperage up to the 100% capacity for shorter time spans.
What this means is for example: A 15A breaker should be able to carry 12 Amps all day long 365 days without having false tripping issues.

Just take the amperage listed for the breaker and multiply by .8 to give you this 80% rating.

So for a 100 amp breaker you shouldn’t load it down over 80 amps. If you don’t want false tripping issues.

If you go over the 80% rule but not 100%. The breaker may hold now while it new. But just give it time and it will start tripping out. I have seen were it takes a year or 2, because the breaker was at 85-90 % loaded.

Hope that helps.


Sent from my iPhone using Tapatalk
 
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,473
Location
Richmond, VA
Just so you know. Most thermal- magnetic breakers. ( the type most residential panels use). Should be able when working properly carry 80% of the amps they are rated for continuously. They can also take amperage up to the 100% capacity for shorter time spans.
What this means is for example: A 15A breaker should be able to carry 12 Amps all day long 365 days without having false tripping issues.

Just take the amperage listed for the breaker and multiply by .8 to give you this 80% rating.

So for a 100 amp breaker you shouldn’t load it down over 80 amps. If you don’t want false tripping issues.

If you go over the 80% rule but not 100%. The breaker may hold now while it new. But just give it time and it will start tripping out. I have seen were it takes a year or 2, because the breaker was at 85-90 % loaded.

Hope that helps.


Sent from my iPhone using Tapatalk

So that makes sense on why the inspector was stating to go with 2/0 wire instead of 4/0. While 4/0 wire is rated for 125A, reality is that the breaker will hold only 100A continuously - so get the wire that matches that. Is my logic sound?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
So that makes sense on why the inspector was stating to go with 2/0 wire instead of 4/0. While 4/0 wire is rated for 125A, reality is that the breaker will hold only 100A continuously - so get the wire that matches that. Is my logic sound?

No youre not making any sense here.

2/0 AL is good for 135a and 4/0 AL is good for 180a NOT factoring voltage drop.

Please go look at table 310.15(B)(16)

A breaker will hold up to its rated value for x number of secs...

The 80% rule applies to the wire.
 