So I am going to be running power out to the shop later next week. It is a 100amp panel. The plan is to run either 1AWG or 1/0 XHHW-2 wire with a 6AWG ground. Larger wire for the voltage drop. The voltage drop with 1AWG is under 2.4% and with 1/0 its under 2% @ 240V and under 5% on 1AWG @ 120V. The price per ft for #1 is .25 cents local and little more for 1/0. It is way cheaper then MHF locally and Im running conduit regardless. I have no interest on pulling MHF nor 90amp max. Looking for a true 100 amp supply without running on the ragged edge. I have a lathe and mill running VFDs, AC Heatpump, LED Lamps, 5HP compressor, 2 welders, plasma, and 2 car lifts. I went down the path with POCO for 400 amp service was not worth pursuing due to cost involved and what they state Im responsible for. I should be able to keep it below 100amps as its a one man shop with a buddy here and there. Cost is under $800 on this route vs 5x that
. Im getting side tracked ... back to the real question.
I know XHHW is supposed to pull better due to the slicker insulation. With the Southwire conduit calculator it says Im in the 26% fill range with 1/0 in 1-1/2 conduit. The run is 130 ft straight with a slight 45 into a 90 before the LB at each end. I dont want to run larger conduit then 1-1/2 unless I have to. Honestly I feel like that should be plenty, but Im looking for a real world analysis from the group. Would you bundle or pull each conductor individually. Last time I pulled 4 conductors bundled 4/0 and it was a PITA. Never pulled on a run like this individually. Anyone have experience with a pull like this? Any regerts
? Thanks.
. Im getting side tracked ... back to the real question.I know XHHW is supposed to pull better due to the slicker insulation. With the Southwire conduit calculator it says Im in the 26% fill range with 1/0 in 1-1/2 conduit. The run is 130 ft straight with a slight 45 into a 90 before the LB at each end. I dont want to run larger conduit then 1-1/2 unless I have to. Honestly I feel like that should be plenty, but Im looking for a real world analysis from the group. Would you bundle or pull each conductor individually. Last time I pulled 4 conductors bundled 4/0 and it was a PITA. Never pulled on a run like this individually. Anyone have experience with a pull like this? Any regerts
? Thanks.