Conduit Wire

nyjets53

Well-known member
Joined
Nov 21, 2007
Messages
87
Location
NY
Is conduit wire the same as romex but with the covering...

At my Lowes it will cost $150 for 3 500 foot rolls of 12 guage wire but only $124 for 500 feet of romex...I need only about 200 feet and then I can use the rest of the romex in the house...

200 feet of conduit wire is almost the same price as the 500 foot rolls...

The new garage door gets installed tuesday, 16 x 7 vinyl, insulated, high lift, and a liftmaster...
 
To avoid these ads, REGISTER NOW!

Bib Overalls

Well-known member
Joined
Dec 4, 2006
Messages
3,318
Location
Jonesboro, Arkansas
No. In simple terms, the rolled wire has a stronger covering that is more resistant to "nicking" and abrasions when pulled over conduit joints and into boxes.
 

OldCarGuy

Well-known member
Joined
Nov 29, 2005
Messages
1,997
Location
Ohio
To code or not,, I would never run romex in conduit. If not for the simple reason that it would be difficult to pull it past any elbows and work boxes,, having solid copper conductors. The single wire you mentioned most likely THHN stranded conductor wire, and more expensive. But the best choice to be pulled through conduit. And best when powering machinery that would transfer vibrations through the wires.
 

chevytruck

Member
Joined
Dec 28, 2007
Messages
24
Location
butte,montana
not to mention romex in conduit can cause overheating, You might call an electrical shop and see if you can buy some half rolls that they have. Or check with electrical supply warehouses.
 

JMURiz

Well-known member
Joined
Dec 6, 2005
Messages
1,483
Location
NoVA
Question:
Could you run romex in pvc conduit if only for operating a switch (ex: so I can turn on my garage lights from inside my house.)?
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
not to mention romex in conduit can cause overheating
I don't agree with that. If it's installed to code there should be no problem.
You might call an electrical shop and see if you can buy some half rolls that they have.
This is the way to go if you're looking for partial spools of thhn.

Question:
Could you run romex in pvc conduit if only for operating a switch (ex: so I can turn on my garage lights from inside my house.)?
Romex can't be run underground or outside. Use thwn wire or UF cable.
If indoors, yes, you can pull romex through conduit though I wouldn't recommend it due to the difficulty of pulling.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,112
Location
Minneapolis
Romex inside conduit is perfectly legal, as long as the conduit is sized properly per NEC. As mentioned it would be a lot harder to install.
 

chevytruck

Member
Joined
Dec 28, 2007
Messages
24
Location
butte,montana
I retract my romex in conduit statement, Just something the local inspector here wont allow, Learn something every day. Guess il stick to the industrial work.

Sorry for the giving wrong info
 

OldCarGuy

Well-known member
Joined
Nov 29, 2005
Messages
1,997
Location
Ohio
I retract my romex in conduit statement, Just something the local inspector here wont allow, Learn something every day. Guess il stick to the industrial work.

Sorry for the giving wrong info

My local inspectors will "red tag" Romex run inside of conduit also.
 

markb1

Well-known member
Joined
Jan 24, 2007
Messages
241
Here in oregon you can run romex in conduit if you size conduit per NEC, but who would want to run say a 1" conduit for 2-#14awg (not that 1" is correct but close).

Then again if you ran UF cable undergrd and come up next to a building you would want to run it in conduit on the building and that would be legal, so there are times that it makes sense.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Someone will correct me if I am wrong but couldn't run the romex with the cover through the conduit.

It is a Bit*h to pull it thru conduit, and if you do you will be hating every minute of it from the time you start till the time you give up. I've done it twice, once in EMT and once in Sch40PVC conduit, and both times I regretted even thinking about it.

Charles
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Romex can't be run underground or outside. Use thwn wire or UF cable.
If indoors, yes, you can pull romex through conduit though I wouldn't recommend it due to the difficulty of pulling.

To clarify what Aceman is saying. A conduit, such as PVC, buried underground or in concrete, is considered a "wet location" (the inside of the conduit) and as such, you could not use Romex, since it is not rated for wet locations.

Usually you pull THHN in conduit. This is also usually rated THWN and is suitable for wet locations (its due to the type of insulation on it). I prefer to use solid #12 THHN and it pulls quite easy. When you get to #10 I use stranded, as solid #10 would be a real bear, though code allows solid #10 in conduit.

Charles
 