You didn't specify what type of wire(AL, CU, compact, regular)...But my 2011 Ugly's book says 5 for regular Al and Cu!
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You can use aluminum for the ground. #1 Al is typically used as the ground in 2/0 Al cable.
The #1 Al should be cheaper than #4 Cu.
 

Ironhorse

Well-known member
Joined
Sep 17, 2012
Messages
800
you can not run 2/0 UF cable in pipe of any kind...it is a ***** for one and in pvc it builds static. On my HV runs I concrete as per spec all the pipe runs for voltage bleeds
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
you can not run 2/0 UF cable in pipe of any kind...it is a ***** for one and in pvc it builds static. On my HV runs I concrete as per spec all the pipe runs for voltage bleeds

Who said UF? I've never seen UF cable in 2/0. Is it actually made that large?
 
OP
D

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
That's how they wrote it.2/0. Verbally said ought. OK. Next question. How so you put slight bends in it. So they sell 45 angles in schedule 40?
 
OP
D

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
2012-09-25_18-51-05_763.jpg
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Look and see what the insulation ratings are that's stamped on the wire. See if it's just USE-2.

Or does it also have RHW-2 or XHHW-2 stamped on it?
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Will look. Direct bury if that means anything

Nope. I'm asking about the insulation rating because you may have wire that can't be run inside. You have to terminate it on the outside in a junction box if it's just USE-2. If it carries the RHH or RHW-2 or XHHW-2 stamp then it's okay to run it inside because it is fire resistant insulation.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Not all direct bury cable are created equal. Some can also be run inside and some cannot. The ones that can be used inside have an insulation that is fire resistant. In addition to being USE-2 the fire resistant direct bury cable also carry a rating of RHH or RHW-2 or XHHW-2.

Had you planned to run this cable to the inside of the structure?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I'll cross my fingers for you and hope it's fire resistant rated. And you are putting it in conduit the whole distance.. right? I can't say I'd lose sleep over using it inside if it's not fire rated, but it would not be to code.

So post back the good or bad news.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
It better be OK. Told them what it was for

The problem is that there is so many different insulation types and grades and not all electricians and people in the trade know about all the different types! So they may have given u something that would work for part of your scenario but not the rest!
 
OP
D

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
OK so when coming out of my house garage. I'm going down with schedule 80 and through the wall. Os it OK to be at ground level just outside the house. Maybe 6 inches before I'm done to the 20 inch mark. Will be schedule 80 anywhere that's exposed to possible damage. 40 under ground.
 