To avoid these ads, REGISTER NOW!

conduit

elba

Well-known member
Joined
Sep 8, 2014
Messages
89
When and why is wiring required to be in a conduit ? Rule of thumb ? Local inspector ? No such thing as a stupid question, right ?
 
To avoid these ads, REGISTER NOW!

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
Are we talking about the wire or where it is located, it is usually done to protect the wire. Most homes have the wire going from the ceiling to the W/H in conduit so you don't have a wire hanging in the air that could be easily damaged. Of course there are lots of other reasons to use conduit. I used conduit in my shop because I wanted to surface mount the wire to make future changes easy and possible. I could not just staple romex type wire to the surface because it would be too easy to damage.
 
Last edited:
OP
E

elba

Well-known member
Joined
Sep 8, 2014
Messages
89
It is a detached pole building about 50 ft. from the house . It is just my car hobby shop.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Country ?? Update GJ Profile with Location.

More details you provide the better advice you'll get from GJ guru's.
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
A general rule is thay if the wire or cable is in a place where it can be easily damaged or touched from the ground then it needs physical protection ie conduit
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,193
Location
The UP, God's country
Local code can be tighter than national codes.

Metro Chicago requires home , and I presume shops, to be wired with conduit.

It's a pain at first, but once you get the hang of bending and routing conduit, it actually looks pretty cool.
 

RoyBell

Well-known member
Joined
Oct 11, 2015
Messages
362
Location
Chicago
It really depends where you live. I would guess 90% of the US you can get away with running romex in the walls (no conduit) In Chicagoland the local box stores don't even sell it because you can't use it anywhere here.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
It really depends where you live. I would guess 90% of the US you can get away with running romex in the walls (no conduit) In Chicagoland the local box stores don't even sell it because you can't use it anywhere here.

Chicago still remembers when Mrs. O'Leary's cow kicked over the lantern in 1871 and their Electrical Codes reflect this.
I think it had a lot to do with Union influence, too.
 

ford33

Well-known member
Joined
Feb 26, 2011
Messages
2,118
Location
Chicago, IL. USA
I like working with electrical conduit. It provides a nice clean organized electrical installation. If I need to make changes to the wire size or number of wires in a conduit, I can easily run new wire in walls and ceilings through the conduit. You cannot do that as easily with Romex stapled to the walls frame.

I live in Chicago and feel conduit is superior to Romex but I am biased. When people ask me who did the electrical installations in my garage, I tell them, I did. What I do not tell them is how much conduit was thrown away because I bent it incorrectly or measured wrong.
 
OP
E

elba

Well-known member
Joined
Sep 8, 2014
Messages
89
xmaxmotorsports not set up for url pics but if you will PM me I will send you some pictures of the Econoline on Yahoo Email
 
OP
E

elba

Well-known member
Joined
Sep 8, 2014
Messages
89
ford33 Do all news homes in Illinois have to have conduit or just Chicago ? Do you use steel or plastic ? About how much $$$ we talking ? Thanks !
 

RoyBell

Well-known member
Joined
Oct 11, 2015
Messages
362
Location
Chicago
ford33 Do all news homes in Illinois have to have conduit or just Chicago ? Do you use steel or plastic ? About how much $$$ we talking ? Thanks !

Pretty much any home within 2-3 hours I believe. I have never worked further than that.

Conduit is steel.

Boxes are steel

The good side is you don't need to ground every device because they are naturally bonded through the conduit system. The wire is also cheaper because you only buy what you need vs romex which sometimes you need 2 wire and sometimes 3 wire.

I am an electrician in Chicago. Conduit goes in fast...after about 4 years of practice. The wiring is very easy compared to romex. I did a house in Wisconsin once and we were allowed to use romex. I hated it. The wire was hard to get into the boxes and you had to ground every device. Sure, we saved on conduit, but then you end up running multiple single wires since you are maxed out with 3 wire romex.

10' of conduit (1/2") is just shy of $2. Fittings are about 15-25 cents each and the metal boxes and ring are about $2-3 bucks combined. #12 ga wire thhn is about $83/1000' from my supplier currently.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Funny how everyone from Chicagoland LOVES EMT, and touts it as the best thing going, and that NM is garbage and no easier to work with, yet the rest of the country knows that it is a joke to run ALL conduit in pretty much any home, and that it is union mandated totalitarian overkill.

I've heard every reason to love conduit, and to hate cable. I have yet to be convinced even a little that conduit is that much better.
"The wire was hard to get into the boxes and you had to ground every device."???? That has to be one of the funniest ones yet.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
A general rule is thay if the wire or cable is in a place where it can be easily damaged or touched from the ground then it needs physical protection ie conduit
You have to remember that Sch40 PVC affords no more protection than NM cable in the eyes of the code.
 

RoyBell

Well-known member
Joined
Oct 11, 2015
Messages
362
Location
Chicago
Funny how everyone from Chicagoland LOVES EMT, and touts it as the best thing going, and that NM is garbage and no easier to work with, yet the rest of the country knows that it is a joke to run ALL conduit in pretty much any home, and that it is union mandated totalitarian overkill.

I've heard every reason to love conduit, and to hate cable. I have yet to be convinced even a little that conduit is that much better.
"The wire was hard to get into the boxes and you had to ground every device."???? That has to be one of the funniest ones yet.

Since your profile states that you are an electrical contractor (as am I), I will give you the benefit if the doubt that you have some knowledge of electrical installations.

The remodel I did was a kitchen. You have 12 ga. solid wiring and multiple circuits. This kitchen I ran 2 small appliance, fridge, microwave/stove, dishwasher and disposal on one. That's 5 circuits.

Lets assume 50' from panel

You need 2 x romex wires. 12-2 @ .22/ft, 12-3 @ .42/ft

$32 in wire.
$5 in stud plates?
$2-5 for wire straps

THHN @ .09/ft
conduit w fittings@ .20/ft

$31 in wire
$10 conduit.

Material is almost identical.

Labor- Both need holes drilled. Conduit goes in quick when you are proficient at it.

Once the conduit is in, one person can pull the wire and you are done.

Romex is a pain pulling one person. Plus if you have to turn corners or pull multiple wires it gets tangled and knotted going through the stud holes. Then you need to double back and nail strap the studs and staple/strap the wires. You are going back 3 times after you make your hole.

Once the wire is in the box with thhn, there is less splicing and terminating. My comment about fitting the wires in the box, it's legit.

2 small appliance circuits, you have 3 wires with thhn. You might have to splice a neutral and a hot, while the other hot blasts right on through. You don't have that luxury with romex. You need to splice all 4 wires. Then you need have a pile of 12ga **** in a box.

4 splices vs 2.

3 wires to terminate vs 2 on a device.

You need to cut the outer jacket and trim the wire vs just trimming the wire.

It's all time and more processes.

What happens when someone wants to add to the house? Pull another circuit or switch a light from another place? What do you do when you have complex setups like 4x3way switches in one box going to different lights? Sounds like a rats nest of wires and trying to ID them is a pain.

What happens if the wire breaks in the wall or gets too short from years of remodeling and you cant get a device on it? You can't just repull the wire. What about a remodel where you can just intercept a conduit and repull the circuit.

Codes are constantly changing. Devices are constantly changing. Conduit really lets people have more options. What are you romex guys going to do when arc fault circuits start taking off by you? It's now an NEC code to have just about every circuit in a house an arc fault. You can't share neutrals so the 14-3 wire is useless and you are now forced to run a bunch of 14-2 cables instead.

Romex works and is just as safe as conduit, but at the end of the day I doubt price difference is more than 5% in either direction. Obviously someone who doesn't work with conduit or thhn on a daily basis will take longer than if they are familiar with romex.

No one needs 500 hp in a car, but you know what, it sure is fun and I rather have it and not need it then need it and not have it :3gears:
 
To avoid these ads, REGISTER NOW!

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
piped houses also burn less. insurance companies in chicagoland know that and have stats to back it up. i don't hate cable, but given the choice i will pipe it every time.
 

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
My house, built in 1935 by the federal government, has conduit for all of the original electrical. Updating the old wire was quick and easy. Adding a conductor for a ceiling fan light also easy. I've grown accustomed to using EMT from running it in my shop. I really like it.
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
Conduit for remodel is great but I can guarantee the cost for electrical on 2 identical houses one in cook county and the other in Florida will be nowhere near the same cost.

Ryan
 

RoyBell

Well-known member
Joined
Oct 11, 2015
Messages
362
Location
Chicago
Conduit for remodel is great but I can guarantee the cost for electrical on 2 identical houses one in cook county and the other in Florida will be nowhere near the same cost.

Ryan

Care to quote your sources? Material will be nearly identical. Pipe is a little more labor on install, but you save on wiring and trimming. Romex is a litttle quicker on the wiring, but you lose it on the trim and fastening of wires.

You can't compare labor RATES, but you can compare labor TIME.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Someone whose opinion I respect stated that EMT was about 20% higher then Romex in costs.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Lotso piped houses in Fla. Lots in older tract block jobs piped on the walls and furred over.
It wouldn't be so practical for wood stud construction without a lot of pre engineering.
On a block job it was super simple and lots of those guys done it before so as soon as the roof was on zoom in and pipe it, smack all the hangers on the wall and the rest of the house could be worked on before it was really wired. No slow staples, multiple cables etc. All the work at floor level except to wire lights.
 
Last edited:

RoyBell

Well-known member
Joined
Oct 11, 2015
Messages
362
Location
Chicago
Someone whose opinion I respect stated that EMT was about 20% higher then Romex in costs.

Is that comparing a person that is proficient at conduit work, or a person that has no idea how to do conduit primarily does romex? 20% seems high to me. Material is only about 25% of the cost of a job, and it's about the same between romex and conduit. The remainder of the cost is labor.

A typical single family here (chicago) is roughly $25,000 for the electric scope (at union rates). That would make labor alone $18,750 and materials roughly $6,250. 20% less cost (material removed) would be $13,750 for labor.

@ $100/hr= 187.5 hrs vs 137.5 hrs = 50 hours difference? That's over a weeks worth of work on a 4.5 week job. Seems high to me and likely comparing a person that might be proficient in romex and not conduit.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Half a dozen or more spools of wire on a cart and a guy feeding fish tape to it and yank every conductor needed in a pull. The devices were screwed into the box and the termination work is super zippy with self grounding.
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
Roping a house around here would easily be cheaper than piping a house here. Labor time and material costs. How much is a guess but I'd bet easily 20 percent or better.
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
2 to 3 dollars for a box and ring plus fittings, romex box is 18 cents. I've done both types of work, for a better quality job I'd pipe it as that's what I did in my barn. If I were looking to get done faster and cheaper, romex for sure.
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
I do have a problem with the "union mandated" comment though. It's not union mandated or pushed. And be happy that there are still unions around your weekends wouldn't be the same without them.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
There are places it could save a lot of work based on technique, mwbc etc, using pipe as ground one could shove 8 circuits in a 3/4, replace 4 cables that might need to be routed and stapled up in a ceiling. Maybe some Jbox could go, this would be highly design dependent.
I saw a guy a while back who did a beautiful job but in several places run 2 pipe where1 would have done with minor design change.
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
The one who I quoted is from the Chicago area & that would be with skilled crews.
 

RoyBell

Well-known member
Joined
Oct 11, 2015
Messages
362
Location
Chicago
2 to 3 dollars for a box and ring plus fittings, romex box is 18 cents. I've done both types of work, for a better quality job I'd pipe it as that's what I did in my barn. If I were looking to get done faster and cheaper, romex for sure.

really?

1 gang plastic box: $.50


plastic 2 gang box: $2.84

Metal box with bracket: $1.03

2 gang mud ring: $.98

So a metal 2gang box setup is $2.01
Plastic is $2.84.

Metal 1 gang setup is $2.01
Plastic is $.50

Boy that's a substantially large difference :willy_nil

Maybe $50-60 more on a single family house?

We know the wire is cheaper than romex and you need less wires and have more options. You can buy colors when you have complicated runs and not have to mark and tag each wire and figure it out later if the marking comes off.

Still not buying the 20% added cost, assuming the romex is installed correctly (nails straps and wire stapled).
 

Ilikeike

ALLIANCE MEMBER
Joined
Jan 8, 2015
Messages
2,452
Location
Northern Ca.
I use to see a lot of "smurf" ENT, in commercial offices(1990s),not just for low volt but 120/208v.
I rarely see it anymore. I always thought that might be a good cheap way to do a home since you could easily add to it when needed,like EMT.
Maybe it's not allowed or cost effective anymore.
 

Redwolf947

Well-known member
Joined
Feb 13, 2015
Messages
613
Location
South East WI
really?

1 gang plastic box: $.50


*****plastic 2 gang box: $2.84*****

Metal box with bracket: $1.03

2 gang mud ring: $.98

So a metal 2gang box setup is $2.01
Plastic is $2.84.

Metal 1 gang setup is $2.01
Plastic is $.50

Boy that's a substantially large difference :willy_nil

Maybe $50-60 more on a single family house?

We know the wire is cheaper than romex and you need less wires and have more options. You can buy colors when you have complicated runs and not have to mark and tag each wire and figure it out later if the marking comes off.

Still not buying the 20% added cost, assuming the romex is installed correctly (nails straps and wire stapled).

*****plastic 2 gang box: $2.84*****

Please note that price is for 20 pcs.. 20 boxes for $2.84.. $0.14 each then??
so the total for plastic is $0.60??
I also see a 2 gang plastic new work box for $0.95. still cheaper
 
Last edited:

RoyBell

Well-known member
Joined
Oct 11, 2015
Messages
362
Location
Chicago
*****plastic 2 gang box: $2.84*****

Please note that price is for 20 pcs.. 20 boxes for $2.84.. $0.14 each then??
so the total for plastic is $0.60??
I also see a 2 gang plastic new work box for $0.95. still cheaper

ahhh, you are right. That 2 gang box also looks like it needs a mud ring to make it work as well. So, $.14 + $.98 mud ring= $1.12 vs $2.01.

Clearly I am not proficient in plastic boxes :lol_hitti

I will bump my price of boxes to $100 more for a single family house :lol:

You will gain it back on the labor side not having to mess with that pesky romex :lol:
 
To avoid these ads, REGISTER NOW!
Top Bottom