Hope someone can help me - I picked up a 40 yo 240V 20A Craftsman compressor, but am having trouble finding a way to plug it into my new garage outlet.

Here's the plug:

20251012_124912.jpg

And here's the outlet the electrician installed for the compressor:

20251012_130311.jpg

The outlet is a NEMA 14-30, rated for 30A, but I can't find an adapter/connector to make the compressor plug work with it.

Is there an existing adapter I can use, or do I need to modify the outlet or the plug?
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
You could use this:


and this or one like it:


Or you could make an adapter cord using a piece of 12/3 SO cord, a 14-30P, and a 6-20C

Or you could put a 14-30P on the end of the compressor cord, you won't use the terminal marked white even though there is a white wire in the cord


Or, even easier is to buy the adapter cord you posted while I was typing everything above.
 
OP
L

lyonkster

Well-known member
Joined
Nov 18, 2009
Messages
433
Location
Portland, OR
You could use this:


and this or one like it:


Or you could make an adapter cord using a piece of 12/3 SO cord, a 14-30P, and a 6-20C

Or you could put a 14-30P on the end of the compressor cord, you won't use the terminal marked white even though there is a white wire in the cord


Or, even easier is to buy the adapter cord you posted while I was typing everything above.

Thanks @sparky 1971. I don't feel like rewiring the outlet (got too many other projects), so I'll just wait for the adapter cord to show up at my door tomorrow (thanks Amazon overnight!).
 

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,057
Location
Fernley, Nevada, about 30 miles east of Reno.
Hope someone can help me - I picked up a 40 yo 240V 20A Craftsman compressor, but am having trouble finding a way to plug it into my new garage outlet.

Here's the plug:

20251012_124912.jpg

And here's the outlet the electrician installed for the compressor:

20251012_130311.jpg

The outlet is a NEMA 14-30, rated for 30A, but I can't find an adapter/connector to make the compressor plug work with it.

Is there an existing adapter I can use, or do I need to modify the outlet or the plug?

The electrician is an idiot......actual electricians know to put the ground pin up for these outlets.
 
OP
L

lyonkster

Well-known member
Joined
Nov 18, 2009
Messages
433
Location
Portland, OR
Amazon to the rescue! :thumbup:

TIP! Turn that receptacle so the ground is on the top……. Turn off the power before working on it.
That adapter cord needs to "hang" without being stressed.
IMG_3250.jpeg

Absolutely, I'd have to flip that outlet if I wanted to use the adapter cord. I think that if I start tinkering with the outlet, I'll just replace the 30A outlet with the 20A Leviton outlet that @sparky 1971 linked above. Cheaper, and cleaner looking, IMO.
 

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,297
Location
Hunterdon County NJ
Absolutely, I'd have to flip that outlet if I wanted to use the adapter cord. I think that if I start tinkering with the outlet, I'll just replace the 30A outlet with the 20A Leviton outlet that @sparky 1971 linked above. Cheaper, and cleaner looking, IMO.
TRUE and easy to do!
I am NOT a fan of those adapters, just another thing that can fail plus they look amateurish.……. Do it once and do it right the first time.
 
OP
L

lyonkster

Well-known member
Joined
Nov 18, 2009
Messages
433
Location
Portland, OR
Don't forget about the breaker...

Thanks, I did forget about that part. Thanks for the reminder that I can't use the 30A breaker with a 20A outlet. Hmm, to swap to 20A outlet and breaker, or flip the 30A outlet and use the adapter cable.... Decisions decisions...
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,268
Location
Coastal NJ
Thanks, I did forget about that part. Thanks for the reminder that I can't use the 30A breaker with a 20A outlet. Hmm, to swap to 20A outlet and breaker, or flip the 30A outlet and use the adapter cable.... Decisions decisions...
I’d keep the 30A receptacle. Rotate it and use the adapter. Some folks would cut the plug off the compressor and put a 14-30P on it.

If you ever need 30A it will already be there.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,948
Location
NJ
You can change the cb, BUT the hardwiring and receptacle is what determines the cb. (Welder recepts excluded.) This is where these adapters create mayhem.

It will be fine as long as the air compressor has OL protection.
 

N_Jay

Well-known member
Joined
Nov 1, 2016
Messages
1,168
Hope someone can help me - I picked up a 40 yo 240V 20A Craftsman compressor, but am having trouble finding a way to plug it into my new garage outlet.

Here's the plug:

20251012_124912.jpg

And here's the outlet the electrician installed for the compressor:

20251012_130311.jpg

The outlet is a NEMA 14-30, rated for 30A, but I can't find an adapter/connector to make the compressor plug work with it.

Is there an existing adapter I can use, or do I need to modify the outlet or the plug?
The problem is someone put a 110v 20A plug on it instead of a 240 20A plug.
Make sure it is really wired for 220 and just remove the wrong plug and put on a correct one.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
The problem is someone put a 110v 20A plug on it instead of a 240 20A plug.
Make sure it is really wired for 220 and just remove the wrong plug and put on a correct one.
Nobody did that. The cord end is a 6-20P. 20 amp 250 volt.

6-20P 20 amp 250 volt:


5-20P 20 amp 120 volt:


Do you see how the horizontal prongs are opposite each other?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
Yeah cause you'll never know when a piece of sheet metal will come sliding down the wall, into the plug and arc off because the main power is wired on the top pin???
Zim
While I am the first one to get pissed off over the ******* ground pin up/down argument, in this case the ground needs to be up because the 90° cord cap should be hanging down when plugged in. As is, the cord would be going up and gravity pulling it over towards the floor.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,268
Location
Coastal NJ
While I am the first one to get pissed off over the ******* ground pin up/down argument, in this case the ground needs to be up because the 90° cord cap should be hanging down when plugged in. As is, the cord would be going up and gravity pulling it over towards the floor.
Agreed 100%. And the adapter the OP proposed has a 90° plug. But if anyone wants to venture there, there is a straight 14-30P available. The Hubbell one is not cheap.
1760362957254.png
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
Agreed 100%. And the adapter the OP proposed has a 90° plug. But if anyone wants to venture there, there is a straight 14-30P available. The Hubbell one is not cheap.
1760362957254.png
I've never seen a straight cap in the wild that I remember but knew they existed. If I remember, I will check pricing through the supply house. The RA cap runs about $20, the same price as the whole adapter. Flipping a receptacle 90° seems pretty simple.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,268
Location
Coastal NJ
I've never seen a straight cap in the wild that I remember but knew they existed. If I remember, I will check pricing through the supply house. The RA cap runs about $20, the same price as the whole adapter. Flipping a receptacle 90° seems pretty simple.
Yes, the straight plugs seem to run $60-120. Crazy. But just in case some future reader is brave enough to install a plug on a cord, but nervous to open up the box and twist the receptacle 180°, there are options albeit expensive ones.

 

duneslider

Well-known member
Joined
Jan 20, 2013
Messages
2,262
Location
Riverton, Utah
Not to totally derail the post but why does the breaker need to be changed? We all have 20amp circuits in our house with 15amp outlets on them with stuff plugged in that pulls less than 15amps. How is that different than a 30amp circuit with a 20amp outlet and a device that pulls less than 20amps? Just trying to understand how this situation is different than the other? (I am not an electrician, nor do I stay at the holiday inn).
 