To avoid these ads, REGISTER NOW!

Connecting stranded to soild with wire nuts?

duneslider

Well-known member
Joined
Jan 20, 2013
Messages
2,261
Location
Riverton, Utah
Just curious what the pro's say is the correct way to connect stranded to solid. Specifically, I just installed a smart switch that required a neutral connection. The line and load (black wires) connected with standard screw terminals just like the original switch but the neutral was a stranded section that needed to connect to the other solid neutrals in the box. The neutrals were all twisted together, I took the nut off and added the stranded in and screwed the nut back on. I gave it a tug and it was secure and then I added electrical tape just to be safe (I was taught that back in the day, not sure if that is good or bad practice).

I have more switches to do. Did I do it right? Should the stranded be twisted around before twisting on the nut? Should I not wire nut and instead use a wago? I have Ideal wing wire nuts from lowes and also 3m wire nuts (just for reference). I notice that a lot of time the stranded wire ends have been soldered. Should I make sure the stranded is soldered first?

Just curious how a Pro approaches these types of connections?
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,596
Location
Long Island
Well, the Wago makes for a painlessly simple way to handle this problem, and for most, perhaps is the safest option.
But we've been mixing solid with stranded under wire nuts for many years, so it IS possible. It's also easy to mess up, but your tug test should let you know if you got everything in there, so long as you did a tug on EVERY individual wire.

What I do is make sure the stranded wire is about 1/16" ahead of any solid wires bundled together before installing the wire nut. And MOST of the time it works just fine, because for the most part, you'll be joining wires of the same gauge. It can get fiddly when you're joining a small stranded wire to a large solid. You need to make sure the stranded makes it into the spring without the solid wire pushing it out of the way at the tip, but don't put so much stranded wire in to clog up the tip of the wire nut and stop the solid wire from being pulled in.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,586
Location
BC
I twist any solids together first with pliers. Then twist stranded around to end at the tip of the solids. Install wire nut.

When it's just one solid and one stranded, a wire nut that's a bit too big won't bite right.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,969
Location
Central Iowa
A lot of it has to do with the quality of wire nuts. The cheap nuts aren't worth a **** and are nothing but an exercise in futility. Everyone has their preference, but I like Ideal. The twisters are my favorite and I go through a ton of tans every year. The orange and gray twisters come in handy outside of the tan's range. I also carry red and blue wing nuts. I will also pre twist the solids if there are more than three, but that's more to make it easier to hold the wad of wires than anything else. Pre twisting the solids also makes it a helluva lot easier to change the dimmer out hot in the future, sparks aren't flying everywhere and lights turning on and off when the solids come apart.
 
Last edited:

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,596
Location
Long Island
This is a non issue. The current on that wire is so low that as long as it doesn't fall out it will never be an issue.
For the ceiling light fixture example this is true, though I wonder if a loose connection would cause nuisance AFCI trips. For the smart switch example it is not necessarily true.
 
OP
D

duneslider

Well-known member
Joined
Jan 20, 2013
Messages
2,261
Location
Riverton, Utah
Okay, so I guess I did it right. I have just seen a few methods used and was curious what pros had to say. I typically always twist solids together before wire nutting. I don't do this stuff professionally so it doesn't hurt me to take a little longer. When I was doing tile and had to pull out backsplash outlets I had a lot of wires pull out of wire nuts but that never happened if the electrician had twisted them. I have also had a handful of wires pull out of the back stabs too. I am also acknowledging that a lot of the issues I encountered were probably from sub-par workmanship.
 

cmandp

Well-known member
Joined
Dec 22, 2011
Messages
1,277
Location
New Jersey
The tug test is essential I think for every connection and every wire in a wire nut.

For stranded wire I usually strip more than normal for solid. Twist the strands and then twist that around the solid wire/wires in a loose helix (maybe 1 to 1.5 turns) and wire nut it.

Usually for things like your smart switch they pre tin the stranded wire(s) which makes it like a solid wire, nice and easy.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,850
anyone crimp the end of the solid for these kinds of connections?

expert diagram:

|
|
\
/
\
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,717
Location
NW Iowa
For the ceiling light fixture example this is true, though I wonder if a loose connection would cause nuisance AFCI trips. For the smart switch example it is not necessarily true.
It's absolutely true for the OP's smart switch. The neutral connection probably has less than 1/100 of an amp on it. It is only running the electronics in the switch. He said the line and load are screw terminals
 
To avoid these ads, REGISTER NOW!

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,311
Location
Dutzow Missouri
I guess I am the only one that “tins” the fine stranded wire with solder before connecting it to a solid wire with a wire nut.

Walta
 

gilbo

Well-known member
Joined
Feb 1, 2010
Messages
716
Well, the Wago makes for a painlessly simple way to handle this problem, and for most, perhaps is the safest option.
But we've been mixing solid with stranded under wire nuts for many years, so it IS possible. It's also easy to mess up, but your tug test should let you know if you got everything in there, so long as you did a tug on EVERY individual wire.

What I do is make sure the stranded wire is about 1/16" ahead of any solid wires bundled together before installing the wire nut. And MOST of the time it works just fine, because for the most part, you'll be joining wires of the same gauge. It can get fiddly when you're joining a small stranded wire to a large solid. You need to make sure the stranded makes it into the spring without the solid wire pushing it out of the way at the tip, but don't put so much stranded wire in to clog up the tip of the wire nut and stop the solid wire from being pulled in.

WAGOs solve nearly all wire joining issues.
I'm with these folks, WAGO and forget about it
 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
Especially when holding the light fixture up with 1 hand while you try to twist the wires together with a nut. Wago makes that easy.

I like the idea of tinning stranded wire end and sometimes find them pre-tinned but don’t really have the time to do that. Maybe if I was retired and the only property I had was my house.
 
OP
D

duneslider

Well-known member
Joined
Jan 20, 2013
Messages
2,261
Location
Riverton, Utah
I have no issue tinning wires if that would be considered a better method. I have a very nice soldering iron and can do it very quickly, and can easily prep them all ahead of time.

If these were new circuits I would consider wago, right now the neutrals are already twisted together and in a wire nut. I am just adding the stranded to it. Going to wago would require additional cutting and stripping (again not a big deal but slightly more time to do) I haven't used wago for home wiring but use them at work for controls wiring quite frequently, mostly for stranded smaller gauge stuff.
 

cmandp

Well-known member
Joined
Dec 22, 2011
Messages
1,277
Location
New Jersey
I'm just a DIYer but I don't use Wagos and I don't bother to tin stranded wire to make a connection.

As long as you have striped enough (but not too much) insulation and are using a correct sized wire nut then do the tug test. I would feel confident to say the connection is good for most anything especially something low current like a dimmer/smart switch or a light fixture.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,596
Location
Long Island
Necro thread brought back, but this caught my eye...
I guess I am the only one that “tins” the fine stranded wire with solder before connecting it to a solid wire with a wire nut.

Walta
Tinning stranded wire with solder has a known creep issue when used in fixed connections such as under screw terminals or in crimps. Whether that's a problem under a wire nut isn't something I can answer, though I'd guess it's fine in wire nuts with metal springs, and potentially unsafe in all-ceramic types.
 

lund

Well-known member
Joined
Nov 2, 2019
Messages
766
Location
Michigan
I twist any solids together first with pliers. Then twist stranded around to end at the tip of the solids. Install wire nut.

When it's just one solid and one stranded, a wire nut that's a bit too big won't bite right.
Exactly. I twist the solids together (lightly) into a wire nut, remove the nut, then twist in the stranded wire following the right handed wrap direction and pre-twist a bit more, then trim the top and put in the wire nut while adding a little extra overall twist. Don't go too crazy with over twisting though or you will complicate any future work. This works well for me even in the most problematic case when joining lighter gauge AL wire for light fixtures with 12 or 14 gauge solid copper. I typically use pliers for the twist. I also give a light pull test at the end to make sure all is ok. I generally prefer NOT to use tape since that can complicate future repairs but I will if I am worried about the security or anything poking in the end of the wire nut.
 
To avoid these ads, REGISTER NOW!
Top Bottom