Please note the 1st part of my comment: "Except for a few exceptions, meters for services over 200A require current transformers.![]()
Around here, 320A has a normal meter. Over that is when you have to go CT.
Please note the 1st part of my comment: "Except for a few exceptions, meters for services over 200A require current transformers.![]()
It looks like 'CT Metering' might be the deciding factor. The service drop, the outside disconnect, meter pans, the giant wiring feeding the subpanels inside- that stuff is long gone and that's what I need to buy. The CT transformers and special meter etc just sound like MORE MONEY to me.
I'll call PoCo again and ask what's the biggest service I can get with direct metering- it might be plenty for me.
Can you have single phase AND 3-phase service in the same building? If that's a possibility, then I could have single phase in the front office part and three phase in the big workshop, two smaller meters instead of one bigger one.
It's late- am I talking all crazy? I'm just excited because next week I get temporary power, and I won't have to power up the place with a generator!
The PoCo engineer lady was extremely helpful- enough to actually make me a little suspicious!
I can run a 320A service with self-contained (direct) metering. I can also have a 200 amp single-phase meter & service to the small upstairs office space- 2 meters, different voltages, from the same service drop. That way when I rent that little space out, the tenant will have a separate meter.
In my case at least, it looks like it's pretty easy & affordable to have 3-phase power in my shop space. Which is good because I bought a 3-phase, 10HP, 18" cutoff saw today at auction for $20. Nobody else had 3-phase power in their playrooms...
Im curious what she meant by different voltages from the same service drop. That doesnt make sense.
This should help clear things up for you.
MTW Ω
I *think* she meant: They will bring the 240V 3-phase to the building, and I can branch one leg off to run through a separate, single-phase 120/240 meter. They only want to bring one service drop per building but she made it seem like I could have 240V 3phase, and 120/240 single phase, going to different parts of the building, through separate meters, from the single service drop. I think.
Clearly I need to do some more homework but when I'm on the phone with the nice lady I have to gauge how far I'm stretching her patience.