I have a pile of contactors, on-off switches, indicator lights etc. One nema 0 contactor lists 480v on the coil, what does this mean exactly? Thank you.
the coil is 480 volts. meaning you need 480 v to energize the coil.
Does the coil control the contactor operation ie latch/unlatch?
That is not a latching contactor, but the coil does operate the contacts, SQ D type S contactors are common, & should be able to be found online. BTW the item pictured is not a contactor, it's a magnetic starter consisting of a contactor & a overload relay.
Okay, so I have a Nema 3 magnetic starter that has a 120v coil but it's from a three phase control panel. The coil only receives power from one 120v phase/leg?
Okay, so I have a Nema 3 magnetic starter that has a 120v coil but it's from a three phase control panel. The coil only receives power from one 120v phase/leg?