Well-known member
My spray foamed building is cooling about 1200 sq feet with 18,000 btu central ac unit. Either the insulation/air sealing is inadequate or that unit isn't working right.
It's a single garage door, and yes insulated... The downstairs part actually has no problem staying cool - but granted, I keep the temp set higher (78). There's no windows down there aside from what's on the garage door itself, I've been pretty happy with that aspect.I assume the garage doors are insulated? There's a lot of leakage and radiant heat through and around most garage doors. When I ran the calculator to cool my 800 SF garage with 11' ceilings, I ended up with a 24k unit. The calculation came in lower, but when I started answering questions about climate, garage doors, windows, etc., it said I needed a bit over 20k BTU. On an extremely hot day in Phoenix, forget it, I can't get it below 90 degrees out there. On a "regular day" when it's below 105 outside I can cool it just fine. I did the drill and fill for the walls and had 18" sprayed in the attic plus DIY insulated the garage doors.
I don't know man... the system has been checked and double checked and it's working fine, and the building was properly spray foam insulated... nothing I can do at this point but up the cooling system to a higher capacity.My spray foamed building is cooling about 1200 sq feet with 18,000 btu central ac unit. Either the insulation/air sealing is inadequate or that unit isn't working right.
Thanks I considered this, but just not sure how to make it make sense - 24000 downstairs alone is waaaay overkill, and this isn't really any less labor than just running a new line upstairs to the larger air handler. Plus the company is taking back my 24k system so I really can't ask for a better deal than that!Short of replacing EVERYTHING, disconnect the unit upstairs. Install a SECOND compressor and new air handler upstairs.
Blocking the stairwell will help a lot.
EDIT : Move the second air handler downstairs, as far away as possible from the first. Most modern systems have a way to "slave" to units together.
Modern mini-splits use inverter drives. It will only consume the power it needs.Thanks I considered this, but just not sure how to make it make sense - 24000 downstairs alone is waaaay overkill,...
It's a single garage door, and yes insulated... The downstairs part actually has no problem staying cool - but granted, I keep the temp set higher (78). There's no windows down there aside from what's on the garage door itself, I've been pretty happy with that aspect.
Yeah I mean my garage itself is bigger (25x28 with 9’ ceilings) and does an OK job keeping 78 degrees with a 12000 btu system. But I think you highlighted my point, it’s just OK. It’ll never get down to 72 on a hot day (and we have a lot of really hot days).Determining actual running capacity in the field can be difficult. If you really want to know for sure, pick up a 12K BTU window unit on Craigslist and throw it in. See what happens. Will probably cost $100 and you can resell it.
To put your capacity in perspective, my garage is 24 x 24 with a 10' ceiling. I finished the garage and I can tell you my insulation is mediocre. Went out the the garage the other afternoon. Was low 90s outside, mid 80s inside. Turned on my 18K BTU thru wall unit, within hour I was comfortable. It made 72* in around 3 hours. I have no doubt I could get away with 12K, possibly 10K BTUs.
If it was adequate it wouldn't have those issues. I cool 1450 square feet with 18k btu single unit and it doesn't struggle at all on the hottest days of the year @ or near 100 degrees.Thanks I'll look into those options. We do have a large section of flat / membrane roof, could I basically paint that elastomeric stuff on top of it? It's black now, so I imagine that could help a lot.
Yeah I'm reluctant as well... but also 12000 BTU just doesn't seem like enough. When I talked to the HVAC subcontractor recently he told me that if he had known what we were using the space for he would have recommended 15000 BTU for sure (slams head into wall).
I honestly don't know for sure, but I believe it's adequate, and regardless... no way I could possibly add more.
Yes, system has been professionally inspected and is performing at max capacity.
It's definitely the stairwell. If I open the door to my third floor, the a/c struggles to keep up. Close it and it's oversizedI agree with everyone else saying something else is going on. I've got around 500ish sq ft with a very similar setup and a Gree 9k unit, though I am partially shaded. Insulation is shabby at best and but the 9k unit will put a hurt on that area. It takes about an hour for it to drop from about 85 to 72 on a 90 degree day.
I think that estimate might only be valid for a single level with 8 ft ceilings. You need to break the spaces up based on ceiling height, then add up the total btu required. So for area with 10 ft ceiling multiply by 1.25, for a 12 ft ceiling multiply by 1.5, for a 16 ft ceiling multiply by 2.It's an enclosed space, except that the staircase coming up into the room is an open stairway. I.e. the room has 8' ceilings, but the staircase has a ~16' ceiling or something, the width of the stairs. So that's probably not helping.
Lots of comments about the insulation being inadequate, maybe. I sure don't know, and can't prove that it is or isn't. It was done by a professional spray foam insulation company that supposedly knows what they're doing. All I can tell you is every square inch of that envelope was spray foamed, so there's no point worrying about it because the only way to add more would be to tear out the entire job and start over... and I guess just rebuild the entire building with a different framing structure to allow for more insulation? I don't know - I appreciate the suggestions but there's simply nothing I can do about that now.
I will look into the white paint on the roof, especially if it can prolong the life of the membrane.
Other than that; I think we're just going to have them upsize the system to 15,000 BTU capacity and hope that solves the issue. I know it's a very rough estimate, but from what I've read you multiply the square footage of the room by 25 to get a rough estimate of the capacity needed. 600 sq ft * 25 = 15000 BTU/h. Doing that math backwards, 12000 BTU/h should cover around 480 sq ft. I think taking into account a sun drenched building in a hot climate we're probably operating on a thin margin, so hopefully bumping up in size will get us some more comfort. We'll see I guess, likely won't know til this time next year as it'll be cooling down soon.
That’s a great idea!How about sealing the door opening with some tape and some plastic to see if it would resolve your cooling issue? If it does you will at least know.
Agree. I'm in TX. Shop (2400 sqft) is cooled by 2 x 24K units. We're spray foam insulated, but it's "marginal" insulation for the area and we've got massive doors. I'd say when it's 108 outside, we can still cool the shop to mid-70s.I have a hard time believing 12,000 BTU will not cool a 600 sqft area that is properly insulated.