Is this ok per electrical code? I would want both switches in the same box. These would control my overhead garage lighting. They are plug in led shop lights.

2c2133b4ad18d30dc4371ea742669128.jpg
 

Attachments

  • 2c2133b4ad18d30dc4371ea742669128.jpg
    2c2133b4ad18d30dc4371ea742669128.jpg
    76.9 KB · Views: 1
To avoid these ads, REGISTER NOW!

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,337
Location
Coastal NJ
If both switches are in the same box, then SW1 switches the red leg and SW2 switches the black leg. Only (1) 3 wire cable goes from the switchbox to the outlet.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,790
You can do it but if in a shop or garage, the receptacle must have GFCI protection.
 
OP
B

bagged89s10

Well-known member
Joined
Mar 13, 2005
Messages
4,607
Location
CT
What if I put a gfci at the beginning of the circuit?. I can install a 3 gang box, run the feed to the gfci, then run power to the switches. Or I can install a gfci breaker.
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
What if I put a gfci at the beginning of the circuit?. I can install a 3 gang box, run the feed to the gfci, then run power to the switches. Or I can install a gfci breaker.
Either way would work. GFI receptacle is cheaper
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
No need for a three gang box unless you just want to. There are dual switches available in both toggle, and decora types. Handles are horizontal.

You may want to use a blank face GFCI if you do not use a gfci breaker since this sounds like it is a lighting circuit only. If you provide an outlet, and a device with a fault is plugged in, you will lose your lights, a minor annoyance.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,790
A GFCI receptacle cannot be split wired like a regular receptacle.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,529
Location
SE MI
If both switches are in the same box make sure the power feed goes into that box. Hot goes to one side of each switch. Black and red come off the other side and feed the separated hot screws on the receptacle.

If you are dealing with existing wiring where the feed goes to the receptacle box, you are going to need 4 wire (or 2 two wire) cables to your switch box (Hot, SW1 out, SW2 out, neutral).
 
OP
B

bagged89s10

Well-known member
Joined
Mar 13, 2005
Messages
4,607
Location
CT
A GFCI receptacle cannot be split wired like a regular receptacle.


Not going to split a gfci. The outlets on the ceiling for the lights will be regular outlets.

No need for a three gang box unless you just want to. There are dual switches available in both toggle, and decora types. Handles are horizontal.



You may want to use a blank face GFCI if you do not use a gfci breaker since this sounds like it is a lighting circuit only. If you provide an outlet, and a device with a fault is plugged in, you will lose your lights, a minor annoyance.


Yes I can get dual toggle switches as well, and I will definitely go with a blank gfci since it will be a dedicated light circuit.
 
To avoid these ads, REGISTER NOW!

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
All garage outlets are required to be GFCI protected.

He could use a GFCI breaker in his garage sub-panel and then wire up a regular duplex receptacle and his switches off of that to achieve what he wants.

This would give him code compliance to GFCI and have control over each outlet via a separate switch.

Jim
 
Last edited:

vtsoundman

Well-known member
Joined
Mar 1, 2016
Messages
69
Location
NorCal
A GFCI receptacle cannot be split wired like a regular receptacle.

All garage outlets are required to be GFCI protected.

Happy to start a new thread, but this seems like it is germane to the discussion.

Some clarifying questions for split duplex :

1. Will code allow separate/split GFCI circuits on a split duplex?
Example : Single duplex on a kitchen counter / garage with two 20A GFCI circuits present using separate neutrals (not a MWBC). No handle tie on the BC breakers.
Answer : ?

2. Will code allow split duplex if a 2 pole GFCI breaker is used in a MWBC?
Answer: This is an acceptable workaround and is often used. Code mandates handle tie/2 pole breaker on MWBC split duplex for conventional circuits.

3. Does code mandate breaker handle tie / 2 pole breaker for two circuits on a split duplex even if the neutrals tabs are also broken?
Answer : ?

4. Will code allow split duplex w/ GFCI circuits if a handle tie is used with two single phase breakers & GFCI outlets?
Example: Two 20A breakers w/ handle tie. GFCI function from two upstream Receptacles feeding a split duplex. Separate neutrals - so no longer technically a MWBC.
Answer : ?

How does AFCI change/affect any of the above?
 
Last edited:
OP
B

bagged89s10

Well-known member
Joined
Mar 13, 2005
Messages
4,607
Location
CT
I ended up using a blank face gfci at the beginning of the circuit.

56c84fafccc541077a8bfa544be379e2.jpg
 

Attachments

  • 56c84fafccc541077a8bfa544be379e2.jpg
    56c84fafccc541077a8bfa544be379e2.jpg
    476 KB · Views: 1

vtsoundman

Well-known member
Joined
Mar 1, 2016
Messages
69
Location
NorCal
These are great too...15 & 20A varieties are available (although I've only ever found 15A switches)

e97b81b5-a3f0-4920-a8cf-f0136525bf58_1000.jpg


40853d1343402235-replacing-gfci-outlet-light-switch-gfciwithswitch1.jpg
 
OP
B

bagged89s10

Well-known member
Joined
Mar 13, 2005
Messages
4,607
Location
CT
What are the 4 switches for?



3 lights on the left side of the garage on switch 1.

3 lights on the right side of the garage on switch 2.

Light over my lathe on 3rd switch.

And 4th switch(currently not wired) will be wired for lights over my main workbench.
 

N_Jay

Well-known member
Joined
Nov 1, 2016
Messages
1,209
Those sound fairly well separated to worry about using a split outlet?
 