control Window AC with thermostat outlet

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
I have a 5000 BTU window AC, I think it draws about 4 amps or so, around 500W. Internal thermostat kind of keeps it around 85F, I want to have the room (not occupied) not go over 100F. I looked into some thermostat controlled outlets and found it. But I want to know if it is ok to just cut the power to the unit suddenly with an external control. Assuming the unit will just resume its last settings when the power is restored.

Because when I had run this unit normally, I can hear the compressor turn off and the fan will continue to blow over the coil for a while when it thinks the set temp is reached, before turning off the fan all together. May have been a similar thing upon startup as well before kicking on the compressor.

If you use an external control you would not have warming up cooling down cycle, and is that bad for the unit? does it really need to cool the coil before turning off the fan?
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,591
Location
Long Island
It's bad for efficiency. When the compressor stops, there's still liquid refrigerant to be evaporated, and the fan should continue to run.
 

Phantomd

Well-known member
Joined
Aug 26, 2015
Messages
183
Location
Near Boulder CO
you have a complicated problem that depends greatly on your particular unit.

Short cycling the compressor is typically bad, thats why there is a delay if you have ever turned the unit off and immediately back on again. now sure how to get around that.

The fan probably runs after the compressor shuts off to evaporate the condensation on the coils.

depending on your need a mini split might solve a bunch of your issues.
 
To avoid these ads, REGISTER NOW!
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
I agree that there is still refrigerant in the coils and blowing on them for a minute may let you extract the last little bit of cool air kind of like turning the AC button off in the car. How much cooling is that from a 5000 BTU system, probably not much.

I just wanted to know if it is bad for the compressor or not to shut the power externally, but it wouldn't be much different from the AC internal control shutting off power to the compressor?

I found an old item I had that is a controller for aquarium and it will be able to turn on a chiller that has high amp so it will handle this small AC as well, and turn it off at 1 degree below the set temp, so I don't need to purchase anything.
 
Last edited:

SALIV8

Well-known member
Joined
Dec 11, 2008
Messages
2,114
Location
chicago and s/w michigan
I wouldn't care about protecting the smallest (and inexpensive) window ac they make. Install the thermostat outlet and be happy. What happens if you have power outages often? Same thing.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Unless it's an old unit with a manual switch, it won't come on when the outlet is powered up. Anything new with digital/keyboard controls will not start after power is applied.
 