Can you remove the outlet from a single gang box and replace it with a knockout faceplate to attach a hardwired appliance whip to?

the outlet is on a dedicated circuit and currently has 14-2 with ground (w/g) wire running to it. Appliance draw is about 4 amps and the breaker is a 15 amp breaker
 
To avoid these ads, REGISTER NOW!

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,769
Location
East Bay SFO
If it’s a dedicated circuit it seems to me that would be OK.
That question makes me and probably other guys curious about what 4 amp appliance needs to be hardwired instead of just plugged in to the existing receptacle. Discourage theft?
 
OP
Z

zc15

Well-known member
Joined
Dec 22, 2020
Messages
433
Location
SE Michigan
If it’s a dedicated circuit it seems to me that would be OK.
That question makes me and probably other guys curious about what 4 amp appliance needs to be hardwired instead of just plugged in to the existing receptacle. Discourage theft?
UL Listed Natural Gas Heater. Originally wanted to put an appliance plug on the heater side to just plug into the outlet, but inspector said no
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,769
Location
East Bay SFO
Gotta keep the inspector happy. That’s a pretty small accommodation to obtain a cleared permit. You might ask the inspector if he/she/they would be satisfied with what you suggested doing. I don’t see why it wouldn’t be OK, but then again, I’m not a licensed electrician.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,630
Location
BC
UL Listed Natural Gas Heater. Originally wanted to put an appliance plug on the heater side to just plug into the outlet, but inspector said no

I assume this is to have a generator run your furnace fan? I would change it and not invite the inspector back.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,201
Location
Modesto, CA
So this is a forced air central furnace?

I cant think of a code reason for this. Did you ask him why?

Furnaces are cord and plug connected all the time
 
OP
Z

zc15

Well-known member
Joined
Dec 22, 2020
Messages
433
Location
SE Michigan
Gotta keep the inspector happy. That’s a pretty small accommodation to obtain a cleared permit. You might ask the inspector if he/she/they would be satisfied with what you suggested doing. I don’t see why it wouldn’t be OK, but then again, I’m not a licensed electrician.
Yeah not happy that the mechanical inspector didnt mention an electrical permit was needed at the time of application

So this is a forced air central furnace?

I cant think of a code reason for this. Did you ask him why?

Furnaces are cord and plug connected all the time
Big Maxx style heater
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
Ask for a code reference for why you can't. One city I work in does have an ammendment that furnaces can't be plugged in, but they don't care about shop heaters.. If he tells you why, and the answer is better than "because I said so", just ask him what he wants to see.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
20,145
Location
Northern Virginia
I had a finished mechanical room with an electric water heater. I had roughed it with a 2-gang box and hung drywall. I used a metal blank plate, drilled it for a Romex connector, and came out of the box with 10/2 Romex to the heater. Right or wrong it passed inspection.

I tend not to argue with inspectors - easy, cave; hard go to the mat.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
Can you remove the outlet from a single gang box and replace it with a knockout faceplate to attach a hardwired appliance whip to
You need a disconnect, which can be a simple snap switch, ahead of the heater unless the heater is in sight from the panel and less than 50'
 
OP
Z

zc15

Well-known member
Joined
Dec 22, 2020
Messages
433
Location
SE Michigan
You need a disconnect, which can be a simple snap switch, ahead of the heater unless the heater is in sight from the panel and less than 50'
Disconnect is the breaker located on wall adjacent to heater. Inspector said it would work since its within reach
 