I didn't say everyone made that assumption but it's a common statement on forums, breaker is only there to protect the building wire.
why was this so complicated?
Run the smallest breaker for the wire! the breaker ONLY protects the wire behind the outlet so its OK to run a load up to 100% of the breaker. De-rating the breaker isn't required. The breaker should be as small as the lightest gauge run.
take out 20A for the 15A breaker, it will be safest for a regular outlet. 20A outlets and plugs are keyed to exclude dollar store extension cords.
a extreme example of what not to do.
1.5KW heater plugged into a thin old 50ft extension cord on a 30A RV circuit. The wire was warm. Breakers do NOT protect loads folks run on jury rigged cords.
more reasons to remove a 20A breaker for a 15A load.20 amp outlets will accept either 15 or 20 amp plugs, including "dollar store" extension cords.
more reasons to remove a 20A breaker for a 15A load.
my main point > its possible to have an extension cord or combination of , that doesn't trip a oversized breaker when shorted.
more reasons to remove a 20A breaker for a 15A load.
my main point > its possible to have an extension cord or combination of , that doesn't trip a oversized breaker when shorted.
note The OP is using a long extension cord instead of fixed wiring. Q: If an imported 12AWG ext. cord is dubiously sourced, can we assume its 100% pure copper. A: No
see note above (post #50)Not precluding the possibility, but pretty remote. Depends on your definition of "oversized. 20 amp on #12 wire is not oversized. Consider the millions of this circuit across the country. If there were a problem it would have been addressed a long time ago.
A direct short will instantaneously trip a breaker.
It should be 14 awg cord for that load and length. Cant idiot proof everything.why was this so complicated?
Run the smallest breaker for the wire! He did 20A for 12 awg, and 20a recept
the breaker ONLY protects the wire behind the outlet so its OK to run a load up to 100% of the breaker. Yes but code says only a device can only be at 80% of circuit rating in multi-outlet ckt. If single recept, then could go up to 100%.
De-rating the breaker isn't required. Where is it derated?
The breaker should be as small as the lightest gauge run. of the premise wiring only and outlet device rating. 12AWG>20A
take out 20A for the 15A breaker, it will be safest for a regular outlet. Not in this case. Im sure it will create nuisance trips. Multiple 15A recepts are allowed on 20A ckts.
20A outlets and plugs are keyed to exclude dollar store extension cords. Alchemist already fixed you up on this detail.
a extreme example of what not to do.
1.5KW heater plugged into a thin old 50ft extension cord on a 30A RV circuit. The wire was warm. Breakers do NOT protect loads folks run on jury rigged cords.
Its possible, but shorts and ground faults typically blow clear and/or trip the cb. Overload conditions, melting insulation, and excessive heat is the bigger watchout causing ignition of adjacent combustible mtls.more reasons to remove a 20A breaker for a 15A load. Not for a motor load that frequently starts.
my main point > its possible to have an extension cord or combination of , that doesn't trip a oversized breaker when shorted.
I agree, its why the small cord comes with a 15 end and not a 30, cant buy a listed cord with the wrong end. Only listed for fault protection to 20A breaker.my main point > its possible to have an extension cord or combination of , that doesn't trip a oversized breaker when shorted.
see note above (post #50)
This is me sizing a breaker for an external circuit and load, not a building code.
There are lots of fires everyday due to things done beyond the outlets/breakers control.
It should be 14 awg cord for that load and length. Cant idiot proof everything.

pfft really? are you using retards logic or what.So if I plug my table lamp (wired with 18-2 zip cord) into an existing 20a circuit receptacle, I should run to the dist. panel and replace the 20a with a 10a?
OCP would be best incorporated into ext cords and individual device cords.
pfft really? are you using retards logic or what.
OCP in line cords? sure thing UK has this, that's called a nanny state.
Using your logic why don't you just change all your 15A CB to 20A youll never have nuisance tripping again. haha
Nope that is wrong. The OP is using an extension cord. Where in this post did the OP ever mention an ext cord? which post? The ext cord was only mentioned for your extraneous heater example only.
A 15A breaker is perfect for his dedicated compressor load. Maybe, but it may trip on startup. And you don't know if he is using a single recept or a duplex. NEC has requirements for these 2 conditions. Oh nevermind, you don't own a code book. Didn't mean to go over your head.
Advising anything less than 12 AWG <50' might infact cause CB tripping.
No one ever advised any ext cord for the Op's purpose.
The solution isn't automatically increasing the CB size! Just because the motor nameplate says 15A doesn't mean its will draw that much for any length of time, so need to derate anything. What is derated?
He already ran #12's to a 20a recept hanging off a 20A cb. Done everyday. Where's the problem? A 20a is better to eliminate startup tripping. I would hope and expect the mfr sized the motor so it is not running at FLA's - but ya never know.
I guarantee if the OP measures the current youll all eat crow for dinner. I doubt anyone cares what the compressor draws as long as it doesnt trip on startup and is not overloaded. You guys took 40+ responses and still don't grasp the OPs situation nor agree with anybody else! Certainly not with you. And you just added a wealth of clarity with no basis. Good Job! Why should it change now![]()
pfft really? are you using retards logic or what.
OCP in line cords? sure thing UK has this, that's called a nanny state.
Using your logic why don't you just change all your 15A CB to 20A youll never have nuisance tripping again. haha
My mom isn't going to touch the outlet or extension cord I have hooked up. It's only her there and no one else to worry about.more reasons to remove a 20A breaker for a 15A load.
my main point > its possible to have an extension cord or combination of , that doesn't trip a oversized breaker when shorted.
note The OP is using a long extension cord instead of fixed wiring. Q: can the homes owner (his mom) replace his extension cord with a much lighter & longer one on his 20A breaker. A: yes it's highly possible.
I'm not sure if the extension cord was mentioned in this thread but it was in another thread I had posted about seeking help when choosing a compressor. My exact setup is a 20A breaker, with a 20A receptacle (with 12 gauge wire) attached to the fuse box in the basement, with a 50' 12 gauge extension cord snaking up the stairs and into the garage.
I can always change it back to a 15A breaker and receptacle. Or just leave it. I am rather curious about the current it will draw so I'm going to order a digital clamp meter and will test it out on Friday when I finally have all my parts and will be breaking it in.
The HF air compressor will run fine on any standard 14 AWG / 15A home circuit as long as the distance from the receptacle to the panel is not outrageously long. I have run these types before with the ceiling light on and even managed to open and close the garage door too.What you've done with 12 AWG / 20A circuit and outlet is more than enough.
These compressors are typically 1.5-1.7 HP but say 2 HP. A true 2 HP compressor will trip a 15A breaker every time. If it doesn't you might have a bad breaker.
Once again this has nothing to do with a code book, no work is being done here that requires an inspection.Oh nevermind, you don't own a code book. Didn't mean to go over your head.
In SoCA, ALL dedicated compressor circuits require both a permit and an inspection.Once again this has nothing to do with a code book, no work is being done here that requires an inspection..

there I fixed it for youIn SoCA, SOME compressor hookups require both a permit and an inspection.![]()
Once again this has nothing to do with a code book, no work is being done here that requires an inspection.
These little compressor motors are designed to be portable E.g run on a 15A household receptacle. It might be problematic when there's extension cords involved and perhaps other loads present. IDK maybe read the compressor manual, some helpful stuff. Most importantly there's a thing called 'duty cycle' requirement. It'll probably tell you not to use an extension cord too, but we are smarter than the average code book waving electrician. If it gives random nuisance trips trouble shoot things by plugging it in closer to the 15A panel breaker, don't just increase the breaker to 20A. The comp. manual warned us or gave a clue about extension cords E.g increased resistance on start-up. The key thing to remember on these compressor is the motor is under more or less constant load so electrically it acts like constant power input. Please let that sink in!
Knowing ohms law and how these motors work on start-up is more helpful than any code book! What would you do without a code book? codebooks are designed for wire pulling apes who memorizes the little bits and pieces that might affect the passing inspection from some other monkey. "ours not reason why, just to do and die." . Perhaps your brain shuts down when reciting code. "over my head" wow yer a legend in your own mind. I probably forgot more about electricity than you've ever known.
The HF air compressor will run fine on any standard 14 AWG / 15A home circuit as long as the distance from the receptacle to the panel is not outrageously long. I have run these types before with the ceiling light on and even managed to open and close the garage door too.What you've done with 12 AWG / 20A circuit and outlet is more than enough.
These compressors are typically 1.5-1.7 HP but say 2 HP. A true 2 HP compressor will trip a 15A breaker every time. If it doesn't you might have a bad breaker.
I find this somewhat amusing based on your posts.
I now have a new appreciation for the saying "To infinity and beyond"
So...is it ok to run a dedicated 20 amp circuit for a 15 amp compressor? Thanks.
That's why I stepped in after 45 posts,I just love these electrical threads, the ones where the OP has a simple question and gets a simple answer in one or two replies. Then, the the pros, semi-pros, advanced do-it-yourselfers, and the occasional troll argue an irrelevant point for four pages. GJ wars.
This electrical forum is plain weird. Strange that some here act like I'm a threat to their livelihood or something, tossing personal insults when I call baloney on their game. I could make a statement like "the sky is blue today" and mmo822 here would argue strongly against it>( WTF guy , this aint king of the hill.. sheesh. Reminds me of fantasy island "da code, da code." lol) Are they using this board to troll for easy work? 
That's why I stepped in after 45 posts,This electrical forum is plain weird. Strange that some here act like I'm a threat to their livelihood or something, tossing personal insults when I call baloney on their game. I could make a statement like "the sky is blue today" and mmo822 here would argue strongly against it>( WTF guy , this aint king of the hill.. sheesh. Reminds me of fantasy island "da code, da code." lol) Are they using this board to troll for easy work?
Id advise anyone to get a second opinion from another source ( a visit from a local electrician will probably be money well spent ) before embarking on any plan of work from this forum.