This is a good thread except for a couple bumps. The idea is to understand some of the fundamental principle of circuit design. The direct answers the op got here are safe and allowed.
you will get shot down every time on this
max load on a 15 amp circuit is 12A.
need to go by nameplate rating not your calculated HP one.
Once again this has nothing to do with a code book, no work is being done here that requires an inspection.
codebooks are designed for wire pulling apes who memorizes the little bits and pieces that might affect the passing inspection from some other monkey. "ours not reason why, just to do and die." . Perhaps your brain shuts down when reciting code. "over my head" wow yer a legend in your own mind. I probably forgot more about electricity than you've ever known.
That depends on the AHJ...regardless, if one doesnt have a code book then how do they know what is to code?
No one ever said that it did? Its obvious you make that **** up to make it seem like you are winning some kind of debate. If that's called talking out of your ***, you must be right since your the expert at it.LMAO talk out of your *** much?
A codebook doesnt tell someone how to pull wire...
No you guys are the know it alls around here, that is why so much energy is focused on trying to beat down others. Stop talking badly about people and help the OP>And BTW the guy you were responding to is an engineer so i doubt you know more than him.... but keep running your mouth like you know it all..

.Yes, that new thread has been a little bit of a trainwreck lol. I'm not bringing anything up to code. The house is a tear-down and will be after my mom sells it. I just need something to suit my needs that won't start on fire or shock anyone
And this thread is still open, and gets longer with more #$%$ in it. By the way @wyliesdiesels is the best. Good clear correct help.

And this thread is still open, and gets longer with more #$%$ in it. By the way @wyliesdiesels is the best. Good clear correct help.
Don't go blowing up wilies head, it big enough already. And so is this thread.![]()

But it is. Not against thermal but against short circuit. A cord wont overheat provided its heavy enough to serve the load, in this case 14, then the breaker needs to be limited to provide adequate fault protection up to any additional protection if it has it within the unit. In the case of 14 wire this would be 30A.A breaker isn't designed to protect any wiring beyond the outlet, so we need to apply a little common sense
But it is. Not against thermal but against short circuit. A cord wont overheat provided its heavy enough to serve the load, in this case 14, then the breaker needs to be limited to provide adequate fault protection up to any additional protection if it has it within the unit. In the case of 14 wire this would be 30A.
This is why we fundamentally,,,,,,,,, (this is why the listing is important,,,, its not always due to the fact that it may overheat the recept) but that the cord and the internals of the appliance are not rated for interruption on larger circuits.
This is why7 the 50 to 20 adapter isn't allowed. Not including the internals,,, but it allows things with a cord smaller than a number 12 (which a 240 v 180A mig has) to be connected to a 50A,,, in this case a compressor with a 14 cord could be plugged in to a 50A circuit.
I agree with some others here, its the code and for good reason and for reasons clearly illustrated in this thread. One doesn't need to have extensive knowledge of every aspect of circuit design, the installer simply follows the instructions. Its also obvious that we got lotso engineers not familiar with this, they may understand way more complex aspects of electrical theory but are sorely lacking in this aspect and it would be easy to cherry pick this thread for living proof of it.
Its also apparent one can get the engineering degree without ever opening the code book, this should be a course requirement, obviously not. (this does not apply to all engineers as a disclaimer) But it can be illustrated from cases where the simple statement that all 50A circuits require a 6 wire. If it was that simple then why he extensive education required. This was from someone that was a wireman before engineer,, wtf did we learn in the school? How in depth did they go in to simple fundamental circuits found in every installation in the country?
^^^^