Yesterday I was under the house working a minor plumbing job, and I happened to run across the electrical wire supplying our heat pump. It seemed a bit small, so I started looking for the label on the Romex jacket, which was really hard to read (faint yellow dots/writing on black pvc jacket, and it was dark). The wire is 8/2, and it is currently fed from a 60-amp breaker (and has been for the last 7 years since the house was built).
The heat pump is 3 ton with 10kW of strip heat. According to the nameplate, minimum circuit ampacity is 74 amps, and maximum overcurrent protection device is 80 amps. So it would seem, at least to me, that this wire is GROSSLY undersized. By the way I’m out in the boonies, so the only permit for the whole house is the state septic permit.
I dig out an (02) NEC handbook, look at article 440, and when I size the wire based on what I see there, I get 3AWG for CU or 2AWG.
Somebody stop me right here if I’m heading down the wrong path (or feel free to tell me I’m on the right one), but I think what needs to be done before there’s any chance of the strip heat kicking on this winter is to upgrade the wire size, as well as the breaker and disconnect.
My current plan is to install an 80 amp breaker feeding 2AWG-2 conductor with ground SER cable (I’m assuming I don’t even want to know how much 50’ of 2-2 copper would cost) that runs to a 100 amp disconnect, then a liquidtight PVC whip containing 6' of 2 -#3 THHN hot conductors and a #8 THHN equipment ground connector. AL wire connections will have noalox.
A few questions
1. Is my wire size correct? Seems like I hardly ever see wire this large used on a residential unit.
2. Any reason that I should not use SER cable?
3. Am I right that once you go over a 60 amp disconnect (~$7) the next step up is 100 amp disconnect (~$70)
4. Does anyone sell a whip with #3 Cu conductors, or will I just need to put one together? (Seems like most of the whips I see are #10 or #8) What size liquidtight conduit would I need to use for this?
The heat pump is 3 ton with 10kW of strip heat. According to the nameplate, minimum circuit ampacity is 74 amps, and maximum overcurrent protection device is 80 amps. So it would seem, at least to me, that this wire is GROSSLY undersized. By the way I’m out in the boonies, so the only permit for the whole house is the state septic permit.
I dig out an (02) NEC handbook, look at article 440, and when I size the wire based on what I see there, I get 3AWG for CU or 2AWG.
Somebody stop me right here if I’m heading down the wrong path (or feel free to tell me I’m on the right one), but I think what needs to be done before there’s any chance of the strip heat kicking on this winter is to upgrade the wire size, as well as the breaker and disconnect.
My current plan is to install an 80 amp breaker feeding 2AWG-2 conductor with ground SER cable (I’m assuming I don’t even want to know how much 50’ of 2-2 copper would cost) that runs to a 100 amp disconnect, then a liquidtight PVC whip containing 6' of 2 -#3 THHN hot conductors and a #8 THHN equipment ground connector. AL wire connections will have noalox.
A few questions
1. Is my wire size correct? Seems like I hardly ever see wire this large used on a residential unit.
2. Any reason that I should not use SER cable?
3. Am I right that once you go over a 60 amp disconnect (~$7) the next step up is 100 amp disconnect (~$70)
4. Does anyone sell a whip with #3 Cu conductors, or will I just need to put one together? (Seems like most of the whips I see are #10 or #8) What size liquidtight conduit would I need to use for this?