Cramp **** connectors for NMB wire?

MatBirch

Well-known member
Joined
Oct 10, 2013
Messages
419
Location
Filer, Idaho
Had to replace my panel in an emergency speed fashion. A leaking meter base on the outside led to corrosion on the neutral bar which created heat leading to arcing and burned wires. The original was very small and overcrowded. The house had been remodeled so many times, that the panel was filled primarily with tandem breakers.
My new panel is much longer, which leaves many of my wires far too short. I know I'm allowed a wire nut in the panel, but it just seems wrong. Short of a huge amount of additional work involving adding a bunch of j-boxes and making extension connections in them followed by bringing all new wire into the panel, is there a cleaner way of splicing wire in the panel?
 
To avoid these ads, REGISTER NOW!

teamo

Member
Joined
Nov 28, 2015
Messages
17
No other way to do it except splices or using a large junction box outside of the main panel and bringing the circuits from the panel into it and making the connections there.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,268
Location
Penngrove, California
I'd use a wire nut before a push on connector. That's just me.

WAGO is more of a lever type clamp connector as opposed to a push on, which I think I would stay away from too, even though they have certainly improved.

Nothing wrong with properly installed wire nut.
 

Syberia

Well-known member
Joined
Jan 13, 2014
Messages
1,451
Location
Perris, CA
These look cleaner than a wire nut because they're in line. They are push on, but I've never had a problem with them.

http://www.homedepot.com/p/Ideal-Sp...sh-In-****-Splices-10-Pack-30-1342S/202894306
 

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,104
Location
central florida
whats wrong with just putting a piece of 4x4 gutter on top of panel the same width
and have all the incoming wires splice there,clean and neat.

I might be wrong but didnt NEC now relax the no splices in a panel board as long as they terminated in it.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
whats wrong with just putting a piece of 4x4 gutter on top of panel the same width
and have all the incoming wires splice there,clean and neat.

I might be wrong but didnt NEC now relax the no splices in a panel board as long as they terminated in it.

Ive never had a problem with splicing wires inside of a panel as long as its done neatly,I do it all the time.;)
 
To avoid these ads, REGISTER NOW!

soj

Well-known member
Joined
Dec 3, 2007
Messages
729
Location
North Georgia
These look cleaner than a wire nut because they're in line. They are push on, but I've never had a problem with them.

http://www.homedepot.com/p/Ideal-Sp...sh-In-****-Splices-10-Pack-30-1342S/202894306

Interesting that the video for this product shows how to install a WIRE NUT! :rocker:
 
OP
M

MatBirch

Well-known member
Joined
Oct 10, 2013
Messages
419
Location
Filer, Idaho
Thanks gang. I finished it up with wire nuts. I have lots of room in my new panel, so I was able to keep it nice and tidy.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
It's OK to splice in a panel as long as there is sufficient gutter space to accommodate them, most panels have plenty of space.
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
Similar question.

Existing is a 60 Amp fused panel with screw in fuses, plus a separate panel for 220V for dryer and range which have been replaced with gas appliances.

New panel will be 200A 30/40 QO.

Would eventually like to rewire the entire house which has no grounded receptacles. And add a sub panel for attached garage.

Will install a new service entrance for the new panel and have a new OH drop.

Should I just feed the existing fuse panel from the new one and then install replacement circuits in the new panel?

I'd like to get all the old circuits out of the fuse panel quicker than that.

Bill
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
I didn't read all the posts, so if I'm being redundant I apologize.

Crimp terminals are not for solid wire.

Tommy
 

Pwrgeek

Well-known member
Joined
Oct 18, 2015
Messages
288
Location
Texas USA
I'd put the new panel in and feed the old one as a sub. Then move everything over as quickly as possible. As for splices inside a panel it wouldn't fly here. I'd mount a large junction box / boxes up near the ceiling and make the splices here.


Sent from my iPhone using Tapatalk
 