Had my final inspection yesterday and passed, but the inspector made a note that he wants an 'irreversible crimp' installed on the ground wires to my panel. Here's the situation: I have 200A service in a steel sided post-frame building which required 3 grounds...two from the panel (one of which also grounds the siding) and another on the opposite corner of the building to ground the siding again. The electrician was off on his estimate of how much #4 ground wire I would need, so he ended up short on the panel and I had to get some more wire. What he ended up doing is running three wires...one from each ground rod and one from the panel and then securing them with a copper split bolt lug. Works just fine, but the inspector wants a crimp (as if someone is going to go in there and unbolt the ground wires). I haven't got a clue where to get a crimp (or what kind of crimp) and crimping tool for this. Does anyone know? Not a big rush; he did pass me but wants to be notified when the crimp has been installed. I'm used to the small gauge stuff for automotive electronics, but not this big stuff.
 
To avoid these ads, REGISTER NOW!

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Code requires continuous, uninterrupted ground to all the rods. The split bolt is not good enough. Exothermic welding is acceptable, an electrical supply house would be able to help you with a one time use kit for this.

Charles
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,681
Location
Maine
Is this a pole building, wooden frame, steel siding? If so its interesting that he made you ground the siding
 
OP
J

Jeepskate

Well-known member
Joined
Apr 28, 2009
Messages
218
Location
Mid-Ohio
Yes, it's a pole building; wooden frame, steel siding.

Thanks for the info, guys. I was trying to avoid calling the electrician since it'll take him longer to drive out here than to crimp it, but I guess he's just going to have to make the trip.
 

Tscott

Well-known member
Joined
Oct 17, 2006
Messages
1,484
Location
Keystone Heights, FL.
Code requires continuous, uninterrupted ground to all the rods. The split bolt is not good enough. Exothermic welding is acceptable, an electrical supply house would be able to help you with a one time use kit for this.

Charles

Charles is correct. Talk to your electrical supply house. They should have a Cadweld kit that will work for you. If not, try google.

http://www.google.com/products?q=ca...esult_group&ct=title&resnum=3&ved=0CCoQrQQwAg


Here is a video, that is similer to what you need. Same process, but instead of a reusable mold the one time kits mold is a throw away.



Tom
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Code requires continuous, uninterrupted ground to all the rods.

It only has to be continuous to the first rod. You can then jump from the first to second rod with another piece of wire.

I've never needed to run 2 seperate wires to two rods, it doesn't make sense really.
 
Last edited:
OP
J

Jeepskate

Well-known member
Joined
Apr 28, 2009
Messages
218
Location
Mid-Ohio
I think I'll go for the crimp since that's what the inspector indicated and the cadweld doesn't seem like such a 'hot' idea for doing right next to a 2x4 wooden purlin. Alternately, I can just dig back down to the ground rods and run two new wires back to the panel. That may actually be my cheapest/easiest route since I can do it myself. Supposed to thaw out on Christmas Eve, so that may be the time to do it.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
Here is a copy & paste from the 2008 NEC, it is unchanged from the 2005 edition.

250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors at the service, at each
building or structure where supplied by a feeder(s) or
branch circuit(s), or at a separately derived system shall be
installed as specified in 250.64(A) through (F).
(A) Aluminum or Copper-Clad Aluminum Conductors.
Bare aluminum or copper-clad aluminum grounding conductors
shall not be used where in direct contact with masonry
or the earth or where subject to corrosive conditions.
Where used outside, aluminum or copper-clad aluminum
grounding conductors shall not be terminated within
450 mm (18 in.) of the earth.
(B) Securing and Protection Against Physical Damage.
Where exposed, a grounding electrode conductor or its enclosure
shall be securely fastened to the surface on which it
is carried. A 4 AWG or larger copper or aluminum grounding
electrode conductor shall be protected where exposed to
physical damage. A 6 AWG grounding electrode conductor
that is free from exposure to physical damage shall be permitted
to be run along the surface of the building construction
without metal covering or protection where it is securely
fastened to the construction; otherwise, it shall be in
rigid metal conduit, intermediate metal conduit, rigid nonmetallic
conduit, electrical metallic tubing, or cable armor.
Grounding electrode conductors smaller than 6 AWG shall be
in rigid metal conduit, intermediate metal conduit, rigid nonmetallic
conduit, electrical metallic tubing, or cable armor.
(C) Continuous. Grounding electrode conductor(s) shall
be installed in one continuous length without a splice or
joint except as permitted in (1) and (2):
(1) Splicing shall be permitted only by irreversible
compression-type connectors listed as grounding and
bonding equipment or by the exothermic welding process.

(2) Sections of busbars shall be permitted to be connected
together to form a grounding electrode conductor.

Bold text by me.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
splices of any kind have to be accessable.and that splice is not code.
 
OP
J

Jeepskate

Well-known member
Joined
Apr 28, 2009
Messages
218
Location
Mid-Ohio
Thanks...I'm aware that it's not code at this point based upon the previous posts and it will be corrected. Good point about the accessability; I'll be sure to put in an access panel when I finish the walls if I don't run new ground wires.
 