Sorry, another compressor thread, but I'm settled on size. I just want some feedback on my plan.
I'm installing a 60 gallon / 3.2 "running" hp compressor.
(Older version of this Husky branded CH, when they were red and had a V-Twin pump rather than the parallel twin)
Photo of motor plate is attached.
Confusing:
Says 15A, though not "FLA".
2.98KW converts to 3.99HP (despite description of 3.2 running HP / 5 peak HP)
240V @ 15A =3600W or 4.8HP
This thing is all over the place...
Regardless, 125% of 15 is 18.75A. I could probably get away with #12 and 20A (or 30A) breaker, but why cheap out? Plus, for inspectors' sake, i'd just as soon use "typical" AWG/breaker size. Not much difference in cost.
Main panel and compressor are both in basement of house.
Compressor is just about 5' from the garage footing.
Panel is about a 20' run from compressor.
(compressor is in the middle, between panel and garage)
Current plan is as follows:
30A breaker in panel. (compressor ran off of a 40' long 12/2 NMD90 "extension cord" on a 30A breaker for years in a hack install at previous home)
10/2 NMD90, 20' or so from panel to j-box attached to ceiling joist next to compressor.
From J-box, transition with Marrettes to #10 THHN in 1/2" EMT about 5' run between ceiling joists through rim joist into garage, to LB box, up wall to switch box.
Leviton MS302 switch, then back into conduit, returning to junction box, and transition to Sealtite whip (or via marrettes to MC) to pressure switch (premounted on compressor).
I originally planned to use all 10/2 NMD90, except the whip end, but figured I would need to bump the conduit up to 3/4" to fit, since the wire would be doubling back, and 2x 10/2 NMD90 = 6 conductor (and 1/2" EMT allows a max of 5 #10 conductors, not to mention the extra sheath of the NMD).
Since it's such a short, straight shot to the garage from the compressor location, I figured I could run it all with a single 10' stick of 1/2" EMT and 4x #10 THHN for the hots to/from the switch and a single #12 THHN green insulated ground.
I would use viration proof, set-screw type, 2-piece Marette connectors for the splices.
Questions I have...
Does anyone have a better idea than transitioning from solid (10/2 NMD90) to stranded (#10 THHN) with Marrettes in the J-box?
I've never used THHN (stranded) on screw terminal devices before. Would it be beneficial to tin the ends?
My understanding, (from synopsis, but I can't find the specifics) per 110.14(A) is that the stranded wire can just be twisted and clamped to screw terminals with retainers..more than 2/3, less than full wrap. I hate strands and even tin the ends of my speaker wire connections to avoid stray whiskers.
On the way back to the compressor. is it better to install a Sealtite whip (flex conduit) and continue the THHN through it to the pressure switch? or transition back to solid 10/2MC at the junction box and run MC to the pressure swtich? I'm leaning toward the former. Stranded wire is better in the flexible section, and eliminates a splice.
Thanks for your patience.

I'm installing a 60 gallon / 3.2 "running" hp compressor.
(Older version of this Husky branded CH, when they were red and had a V-Twin pump rather than the parallel twin)
Photo of motor plate is attached.
Confusing:
Says 15A, though not "FLA".
2.98KW converts to 3.99HP (despite description of 3.2 running HP / 5 peak HP)
240V @ 15A =3600W or 4.8HP
This thing is all over the place...
Regardless, 125% of 15 is 18.75A. I could probably get away with #12 and 20A (or 30A) breaker, but why cheap out? Plus, for inspectors' sake, i'd just as soon use "typical" AWG/breaker size. Not much difference in cost.
Main panel and compressor are both in basement of house.
Compressor is just about 5' from the garage footing.
Panel is about a 20' run from compressor.
(compressor is in the middle, between panel and garage)
Current plan is as follows:
30A breaker in panel. (compressor ran off of a 40' long 12/2 NMD90 "extension cord" on a 30A breaker for years in a hack install at previous home)
10/2 NMD90, 20' or so from panel to j-box attached to ceiling joist next to compressor.
From J-box, transition with Marrettes to #10 THHN in 1/2" EMT about 5' run between ceiling joists through rim joist into garage, to LB box, up wall to switch box.
Leviton MS302 switch, then back into conduit, returning to junction box, and transition to Sealtite whip (or via marrettes to MC) to pressure switch (premounted on compressor).
I originally planned to use all 10/2 NMD90, except the whip end, but figured I would need to bump the conduit up to 3/4" to fit, since the wire would be doubling back, and 2x 10/2 NMD90 = 6 conductor (and 1/2" EMT allows a max of 5 #10 conductors, not to mention the extra sheath of the NMD).
Since it's such a short, straight shot to the garage from the compressor location, I figured I could run it all with a single 10' stick of 1/2" EMT and 4x #10 THHN for the hots to/from the switch and a single #12 THHN green insulated ground.
I would use viration proof, set-screw type, 2-piece Marette connectors for the splices.
Questions I have...
Does anyone have a better idea than transitioning from solid (10/2 NMD90) to stranded (#10 THHN) with Marrettes in the J-box?
I've never used THHN (stranded) on screw terminal devices before. Would it be beneficial to tin the ends?
My understanding, (from synopsis, but I can't find the specifics) per 110.14(A) is that the stranded wire can just be twisted and clamped to screw terminals with retainers..more than 2/3, less than full wrap. I hate strands and even tin the ends of my speaker wire connections to avoid stray whiskers.
On the way back to the compressor. is it better to install a Sealtite whip (flex conduit) and continue the THHN through it to the pressure switch? or transition back to solid 10/2MC at the junction box and run MC to the pressure swtich? I'm leaning toward the former. Stranded wire is better in the flexible section, and eliminates a splice.
Thanks for your patience.