Crouse and hinds main breaker upgrade

sickboi55

Well-known member
Joined
May 3, 2008
Messages
185
I'm in the process of trying to get all my ducks in a row for adding a detached shop. I have a crouse and hinds breaker panel with a 150 amp main breaker. The feeder from the meter will support 200 amps. The concern is whether or not my panel will accommodate it. Can someone help me determine if I can add a 200 main breaker to my current panel? I don't want to add a new panel if it isn't required. I will be farming out the work but would like to know what to expect. Thoughts?
 

Attachments

  • 20240112_193643.jpg
    20240112_193643.jpg
    543.8 KB · Views: 24
To avoid these ads, REGISTER NOW!

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,275
If you are going that far just replace it with a QO panel. Breakers are easier to get and panel is better and cheaper.
 
OP
S

sickboi55

Well-known member
Joined
May 3, 2008
Messages
185
The issue with replacing the panel is it is currently located in a non-approved location. It is in a kitchen cabinet. I don't know if that was ever allowed but that is what I have. The cost to move it will be VERY prohibitive.

For the load calc. That is sometjing I have not done, but I plan to run a 7.5hp compressor, plasma, and welder in the shop so the need for 100 amp is real, even for 1 person. I am, however, on gas for dryer, hot water and stove in the house.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Those Crouse-Hinds/Murray breakers have a bad reputation, and are you sure the wiring can support a 200A breaker?
 
OP
S

sickboi55

Well-known member
Joined
May 3, 2008
Messages
185
Those Crouse-Hinds/Murray breakers have a bad reputation, and are you sure the wiring can support a 200A breaker?
I am 100% sure the feeder from the meter can support 200 amps. It is 4/0 cable.
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
For the load calc. That is sometjing I have not done, but I plan to run a 7.5hp compressor, plasma, and welder in the shop so the need for 100 amp is real, even for 1 person. I am, however, on gas for dryer, hot water and stove in the house.

Simultaneously?

Do a load calc, you be surprised. Even if you're using 100a in the shop I bet the house is fine on 50a.
 
OP
S

sickboi55

Well-known member
Joined
May 3, 2008
Messages
185
I went into the attic to double check, the feeder is aluminum. So I double checked some online amp charts and it turns out I was 100% wrong. My feeder is only good for 180 amps. Unless I am reading the chart wrong.

Doing the load calculation, I got in the mid 70's.
 
OP
S

sickboi55

Well-known member
Joined
May 3, 2008
Messages
185
The charts I found say that XHHW 4/0 2 conductor aluminum cable is good to 180 amps. I trust what you are saying, and I am happy that I won't need to run new feeder, but can help me understand where my search led me astray?

For the main breaker, my research indicates the Siemens QS series is the recommended replacement. Any issues there I am not seeing?
 
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
The charts I found say that XHHW 4/0 2 conductor aluminum cable is good to 180 amps. I trust what you are saying, and I am happy that I won't need to run new feeder, but can help me understand where my search led me astray?

For the main breaker, my research indicates the Siemens QS series and the recommended replacement. Any issues there I am not seeing?
There is an exception for when it feeds the entire load of a dwelling.

Same goes for #2 Al. It's only good for 90a to a subpanel, but 100a as a feed to a dwelling
 
OP
S

sickboi55

Well-known member
Joined
May 3, 2008
Messages
185
Isn't the one I linked the one made for your panel?

I wouldn't touch it until knowing that 150 won't work
The one you linked is used, and broken. That is why I am asking about the QS series being the correct/approved replacement.

Why not touch it? Are you saying run the 100 subpanel and if it becomes an issue then replace the main?
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
NEC 240.4
(B) Overcurrent Devices Rated 800 Amperes or Less. The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted
to be used, provided all of the following conditions are met:
(1) The conductors being protected are not part of a branch circuit supplying more than one receptacle for cord-and-plug connected portable loads.
(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjustments).
(3) The next higher standard rating selected does not exceed 800 amperes.
 