I purchased a 20kw PTO generator for my tractor, and I'm adding a digital frequency meter/voltage/current/etc. to it. The current portion uses a single current transformer.

If I put both hot legs through it, will I see the sum of the current, or the difference? I believe they cancel out, so if was 20A/20A flowing through I would see 0A since they are opposing phases, but I want to make sure.

Need to know if I'll need to have two (one per phase) or if one is sufficient.
 
To avoid these ads, REGISTER NOW!

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Only one leg. Can't be neutral unless you want to measure the difference between the two legs. So you will need two meters (one for each leg...)
 
To avoid these ads, REGISTER NOW!

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
If you run both legs thru the ct you will see the difference in the two. Be careful with the toggle switch as cts become step up voltage transformers when disconnected from the circuit. This can cause a flash over and destroy expensive things. Any ct on a live circuit must either be loaded or shorted, never open.
 