Hi I have a Cutler Hammer main panel i am looking for a circut breaker 50 amp that can feed a 1/0 wire or is there a reducer :headscrat
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,755
If you are oversizing your wire & running a equipment grounding conductor, you have a serious issue w/ 250.122(B) here is a copy & paste from the 2008 NEC.

(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.
 

mtne

Well-known member
Joined
Dec 3, 2007
Messages
113
Location
Denver
Little more details please? The lugs in jasons link would need a special crimp tool to do what they are designed for......
 