If I had this problem to solve: What I want is a photoeye, check Banner Engineering for a large selection. I feel that SICK, Pepperl+Fuchs also are competitors which will have a similar selection. You mount it opposed to a reflector, the PE gets mounted on one column, the reflector on the other column. In normal state, the PE "sees" the reflection, so, If the light beam is broken then the internal normally-closed (NC) contact changes state this inhibits power to your "jog up" contactor. Probably easiest if the PE uses 120vac but you will find a lot of them that use 24vdc, necessitating a low amp power supply and a 24vdc-coil relay.
Ideally mount PE and reflector on unistrut so the distance below the ceiling is easily adjustable.
Also...suppose you jog the lift into the situation where it is stopped. Now you have to get it out of that condtion, and might have to jog up some slight bit more to get the latch(es) released. So you will probably need a momentary pushbutton or keyed switch to override/bypass/jumper the inhibiting effect of the NC contact going open. Choose very carefully when actuating the PE override button.....
Additional fanciness would be an indicator light to denote that this is the problem so one doesn't jump to other conclusions like the power is out, breaker tripped, start cap has burned up on the motor, etc, etc.
If this seems interesting I will draw up some ladder logic.