He did not use the blue spray at all. On the outside unit, he claimed that if there is a leak while pressurized to 600 psi, you will hear it.Im not a pro.
How are the flare connections at the indoor units? He just listened for a leak only? My tech used blue spray to watch for bubbles at each connection.
The system was low on refrigerant. The first time the tech hooked on the manifold, the high (liquid) side reads 80 psig, and the suction side reads 0.I'm confused ..... when you switched to AC .... was it still heating?
Are the three heads all back to the outside unit or do you have a branch box?
Unless the thing never worked ... I would be surprised if the problem was a failed line. Typically they get damaged when the drywall goes in ... lines can fail -- but not normally in a year.
The tech only pressurized the system with nitrogen (not R410A) to test.My guess is a flare failed to hold .... IMO this is the main problem with a mini in the USA. The flare. In much of the world they are all surfaced mounted and the lines exposed ... or mostly exposed. We in the USA like our equipment hidden -- when anything happens -- it's a big deal. I'm in this camp as well ... I hid mine ...but, I make sure that we can get to the fittings some how without ripping too much apart.
Any one of the joints can be the problem ... since there really is no high low on the lines to the heads with the direct piping .. I'm not sure what he was checking.
So the guy never used a tester to test for refrigerant ? You fill the unit and test for the presence of refrigerant .... while also looking for ant leaks. I have heard of guys .. just redoing all the flares.
It's sad .... these things just run for years ... especially the quality units. It's the leaks that cause the problems ... I have been lucky and have never had one leak. Naturally the multi head have more places to do the system in.
All zones are not cooling / heating (I tried both cooling and heating). In addition, the remote diagnostic code shows U0, which means "refrigerant shortage".In the picture, there are 3 zones & therefore 3 solenoids that open to allow refrigerant to the zone that needs conditioning.
The solenoid may not be opening....
Does the heating or cooling function operate in any other zone?
Does the cooling work in the questioned area or is that compromised as well.
All zones are not cooling / heating (I tried both cooling and heating). In addition, the remote diagnostic code shows U0, which means "refrigerant shortage".
Yes, it worked before. Both cooling and heating. It was in August when I noticed it wasn't cooling.Did the system ever work? ..... since you talk about heating .... it must have heated ... correct?
I always run them like crazy when they are first installed ...
Yes, it worked before. Both cooling and heating. It was in August when I noticed it wasn't cooling.
Thanks for the suggestion. Yes, checking the air handler flares joints should be next for the new tech I need to find. The drywall would need to be cut to check those flares.At the pressures they work -- it would have to be a rare hit with a drywall screw to not leak out quickly.
Can you get to and see all the flare fittings if need be.
I had one install where I had no choice but to burry the joint a few feet from the unit ... there was no way to fish the short tubing from the head any other way. I boxed out square and had it open after the drywall was done. We hung the unit and I ran and tested everything. I had thought about using one of those plastic doors as the unit was obscured from most of the space ... ended up putting the drywall square back in and mudding it in ..w/ pictures.
I think the solution you may be faced with is redoing all the flares. Hope he did not extend any lines. I guess the original installer is not paying for nay of this .... that's a quality unit and I'm sure not cheap
Thanks for the suggestion. Yes, checking the air handler flares joints should be next for the new tech I need to find. The drywall would need to be cut to check those flares.
In the original install, the installer did not sweat/make joints to extend the linesets. The three linesets were each a contiguous 50-ft and then shortened to length outside.
Well, the tech's suggestion was to braze service ports onto each of the linesets on the outside, then pressurize each lineset separately. This will tell us which lineset is bad. We would then have to cut the drywall of the corresponding lineset to check / replace.Also -- how did he point to a line being damaged or leaking when he could not get to all the joints ?
SALIV8, thank you for the suggestion. I was planning to get one from DaikinAs i said before scanchain, check your local energy company rebates. They will have a list of qualified contractors if they offer any money back on mini splits.
Also this just dawned on me. Call ecomfort.com and see if they can recommend anyone in your area. I believe they have contacts all over.
Id also be searching yelp and other review sites for ductless ac installers.
Well, the tech's suggestion was to braze service ports onto each of the linesets on the outside, then pressurize each lineset separately. This will tell us which lineset is bad. We would then have to cut the drywall of the corresponding lineset to check / replace.
Mesozoic & floridafarmer, thanks for the offers, I appreciate it very much. Unfortunately, I'm actually located in N Atlanta suburb, not in FL.
OP here. I had another contractor come and investigate the problem. He was recommended by a friend and this contractor used to work on mini-splits for many years outside of the US. He came with a refrigerant leak detector (sniffer). Browsing on Amazon, I think he was using the INFICON D-TEK Select, Refrigerant Leak Detector, 712-202-G1, rated to detect a leak of 0.10 oz./year
https://www.amazon.com/dp/B00063VK6Y/?tag=atomicindus08-20
After he filled the linesets with R410A, the detector was able to detect two leaks at the flare connections to the air handlers.
After fixing the bad joints, evacuating and re-charging with R410A, the system appears to be running correctly now. Hopefully it stays this way.
Looking back, the installer really did a bad job with the flare connections at the air handlers. He made not one, but two bad joints. The earlier suspicion about a screw possibly puncturing a lineset turned out to be incorrect.
Thank you everyone for the suggestions and support.
I agree. Luckily I stepped back and went for a second opinion when the initial repair guy suggested to braze service ports onto the linesets. That would have created a mess.sad you had both a bad install and a second who did not have the knowledge or equipment to do the job either ... naturally everybody wants to be paid as if the are of the highest caliber.
Just think if you would have followed the second guys advise ...
I agree. Luckily I stepped back and went for a second opinion when the initial repair guy suggested to braze service ports onto the linesets. That would have created a mess.